Ze is done at the origin of the installation with either a 2 lead or 3 lead test using an earth fault loop impedance tester with the installation turned off and the earth disconnected to eliminate parallel paths. PFC is similar (meter on different setting) but with all potential parallel paths in place (ie earth reconnected).
 
You don't have to measure PFC (PSSC) on a radial circuit (unless it's a distribution circuit).

Not sure why you need to measure Ze on a radial (unless as above), but you could do a loop test to find out Zs then do a continuity test find out (R1 + R2)
Then
Ze = Zs - (R1+R2)
 
Disconnect the main earthing conductor at the MET and using an earth fault loop impedence tester connect to the line supply side and to your disconnected main earth and carry out your Ze test.

For PFC you need to test PEFC (prospective earth fault current) and PSCC (prospective short circuit current). To test PEFC you must connect line/earth supply side, to test for PSCC you connect line/neutral. Record your highest result.
 
Last edited by a moderator:
If its a TNCS system you can also calculate the PFC as the neutral of the supply is used as a protective earth and neutral (PEN). When you have obtained your EFLI, you can convert it to PSCC by using the following equation:

PSCC = V/Ze = I

for example if your Ze is measured at 0.37: 230/0.37 = 621.6 amps
 
you did

For PFC you need to test PEFC (prospective earth fault current) and PSCC (prospective short circuit current). To test PEFC you must connect line/earth, set tester to "no trip" if RCD is present, to test for PSCC you connect line/neutral, again, "no trip" if RCD is present. Record your highest result.
 
don't worry. the man who never made a mistake , never made anything. i nce fittede 12 halogen floods on a driveway of a posh house, then lamped them up with 110v lamps. was like chinese crackers.
 
I was working in a conference center in Brighton once and a bloke wired up ALL the 12v halogen spotlight transformers in the main hall back to front. That was a hell of a show when those got turned on. I've never seen so many grown men scream. Lol.
 

Reply to domestic radial in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
138
https://www.amazon.co.uk/gp/product/B08CJ3VC79/ref=ppx_yo_dt_b_asin_title_o05_s00?ie=UTF8&psc=1 I use this, current clamps go round each outgoing...
Replies
3
Views
492
  • Question
Why aren't you asking them?
Replies
5
Views
783
  • Question
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks