do you mean Zs? Ze is measured at source, nothing to do with a circuit as regards measuring Ze.
 
Ze is done at the origin of the installation with either a 2 lead or 3 lead test using an earth fault loop impedance tester with the installation turned off and the earth disconnected to eliminate parallel paths. PFC is similar (meter on different setting) but with all potential parallel paths in place (ie earth reconnected).
 
You don't have to measure PFC (PSSC) on a radial circuit (unless it's a distribution circuit).

Not sure why you need to measure Ze on a radial (unless as above), but you could do a loop test to find out Zs then do a continuity test find out (R1 + R2)
Then
Ze = Zs - (R1+R2)
 
Disconnect the main earthing conductor at the MET and using an earth fault loop impedence tester connect to the line supply side and to your disconnected main earth and carry out your Ze test.

For PFC you need to test PEFC (prospective earth fault current) and PSCC (prospective short circuit current). To test PEFC you must connect line/earth supply side, to test for PSCC you connect line/neutral. Record your highest result.
 
Last edited by a moderator:
If its a TNCS system you can also calculate the PFC as the neutral of the supply is used as a protective earth and neutral (PEN). When you have obtained your EFLI, you can convert it to PSCC by using the following equation:

PSCC = V/Ze = I

for example if your Ze is measured at 0.37: 230/0.37 = 621.6 amps
 
Its a solar installation and the radial is in fact a back feed from the inverter im using a standard installation cert it asks for pfc and external loop impedance Ze
 
Ze is the earth loop impedance at the mains source. Eg the meter. Nowhere else. The e stands for external (ie outside the building). You can't measure it on the end of a circuit.
 
you did

For PFC you need to test PEFC (prospective earth fault current) and PSCC (prospective short circuit current). To test PEFC you must connect line/earth, set tester to "no trip" if RCD is present, to test for PSCC you connect line/neutral, again, "no trip" if RCD is present. Record your highest result.
 
don't worry. the man who never made a mistake , never made anything. i nce fittede 12 halogen floods on a driveway of a posh house, then lamped them up with 110v lamps. was like chinese crackers.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
domestic radial
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
karmannmann,
Last reply from
SPARTYKUS,
Replies
18
Views
3,458

Advert

Back
Top