Hi All,
Been called to a customer property for nuisance tripping which i have resolved but when inspecting installation i have found an issue.
The customer has a cabin at the back of the property with a CU inside, fed by 10mm SWA. it has 32a RM, another 32a (still locating its purpose), 16a radial, 6a lighting and a 6a boiler. This is fed from a 32a MCB in the property CU. this isn't sufficient both due to diversity and it physically keeps tripping.
I want to split off the tails in the house but my question surrounds fusing,
I want to put small RCD unit below the CU fed with separate tails just to the cabin. please see crude diagram below of my intentions.
house CU with RCD
/
Cutoff ---- fused switch ----- service connector
\
RCD ----(SWA)-- Cabin CU
my question surrounds fusing of leg to cabin CU, If I put an MCB diversity is gone for the cabin submain, so i'm pondering on what to do, would the fused switch suffice??
NIC were dog toffee when posing.
Been called to a customer property for nuisance tripping which i have resolved but when inspecting installation i have found an issue.
The customer has a cabin at the back of the property with a CU inside, fed by 10mm SWA. it has 32a RM, another 32a (still locating its purpose), 16a radial, 6a lighting and a 6a boiler. This is fed from a 32a MCB in the property CU. this isn't sufficient both due to diversity and it physically keeps tripping.
I want to split off the tails in the house but my question surrounds fusing,
I want to put small RCD unit below the CU fed with separate tails just to the cabin. please see crude diagram below of my intentions.
house CU with RCD
/
Cutoff ---- fused switch ----- service connector
\
RCD ----(SWA)-- Cabin CU
my question surrounds fusing of leg to cabin CU, If I put an MCB diversity is gone for the cabin submain, so i'm pondering on what to do, would the fused switch suffice??
NIC were dog toffee when posing.