Double pole isolation or switching on a TT system would be achieved by the main switch.
There is nothing wrong with installing single pole RCBOs on TT systems however if there was an s-type up front, you would need to install double pole RCBOs if RCBOs were specced for the job.
Why D ?
Most upfront S-types are DP/Multi-pole anyway, I have seen these double up as the Isolator too, in fact on the model forms there are boxes to fill in where the RCD is used as a mains switch.
Just curious to your reasoning as to why you would need DP RCBOs in the above scenario where an upfront DP or multipole S-type RCD is used.
N-E fault on the single pole RCBO protected circuit will take out the upstream type-s too. So much for minimising inconvenience in the event of a fault! lol
What they are trying to say is RCBOs are single pole and should not be used where double pole is required, They are not saying do not use on tt, why would they?Manufactors instruction leaflet states {on schneider electric rcbo)
Do not use on installations that require double pole switching eg IT or TT.
Think you'll find those RCBO's may well be SP+N rather than douple pole in the true sense of the meaning...