Manufactors instruction leaflet states {on schneider electric rcbo)
Do not use on installations that require double pole switching eg IT or TT.
 
What they are trying to say is RCBOs are single pole and should not be used where double pole is required, They are not saying do not use on tt, why would they?

I think they are......In a TT installation neutral is also classed as a line conductor,And as such if isolation to a particular circuit is required for maintenance or alteration we are supposed to be able to isolate both poles without having to knock the whole installation off via the mainswitch RCD. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.
 
I think they are......In a TT installation neutral is also classed as a line conductor,And as such if isolation to a particular circuit is required for maintenance or alteration we are supposed to be able to isolate both poles without having to knock the whole installation off via the mainswitch RCD. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.

Because it isn't an issue. DP isolation is all that is required on a TT installation, it doesn't say where. Also, a neutral is never a line conductor.
 
[ElectriciansForums.net] don't use rcbos for TT
Originally Posted by mrloy99 [ElectriciansForums.net] don't use rcbos for TT

. I am thinking that double pole CBs could be the answer(rather than dp rcbo's) I know that they are available,and you are still 30ma protected via main switch rcd. I'm a wee bit surprised mr Niceic hasn't made an issue about this before.

Far more sensible to have an all RCBO (SP+N) CU, than a couple of RCD's and a rack of DP MCB's, on a TT installation!!

Also have you considered the size that 10 circuit DP CU will be?? You'll be looking at providing at least a 26 way CU, including the DP isolation switch and 2 X RCD's, and that's not allowing for say a couple of spare ways for the future!! ...You won't be purchasing one of them for 50 odd quid!! lol!!
 
Last edited by a moderator:
Because it isn't an issue. DP isolation is all that is required on a TT installation, it doesn't say where. Also, a neutral is never a line conductor.

Sorry meant to say live..rather than line, neutral IS classed as a live conductor.
And without getting too ---- about the whole thing....We have to consider all possible scenarios.
We may wish to do work to a particular circuit without turning off the whole board.It is unlikely that all circuits have isolation after the board. eg lighting circuit with 2way switching
In TT situations neutral is not considered to have a RELIABLE connection to earth(unlike TN.where neutral and earth are joined at the service head)It is possible for the neutral to have a higher potential than earth .Removing the assumed neutral from the neutral bar is not recommended also due to a few possibilities,eg borrowed neutral or neutral in the wrong terminal in the neutral bar.
This voltage may only be a few volts and is unlikely to kill you but an unexpected tickle while working over the stairwell in a house could cause a fall.
 
Far more sensible to have an all RCBO (SP+N) CU, than a couple of RCD's and a rack of DP MCB's, on a TT installation!!

Also have you considered the size that 10 circuit DP CU will be?? You'll be looking at providing at least a 26 way CU, including the DP isolation switch and 2 X RCD's, and that's not allowing for say a couple of spare ways for the future!! ...You won't be purchasing one of them for 50 odd quid!! lol!!

Dunno about that!!!
The dp cb's I was using today(in an IT installation)were single module,same phisical size as normal cb's(general electric)
 
Dunno about that!!!
The dp cb's I was using today(in an IT installation)were single module,same phisical size as normal cb's(general electric)


That's true, but then most journeyman electricians don't know that they even exist.

I know that a guy is importing them from here (China) on another forum. How about giving us a link to these GE single module DP breakers, for everyone to see....
 
That's true, but then most journeyman electricians don't know that they even exist.

I know that a guy is importing them from here (China) on another forum. How about giving us a link to these GE single module DP breakers, for everyone to see....


i dont have a link but i could prob take a photo.They come inside these ips pre built bespoke panels made by a company called bender in uk.(I think they are german,but operate globally.)
 

Reply to don't use rcbos for TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
612
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K
  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3
Replies
65
Views
6K
Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
6K
suffolkspark
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks