whats classes as the correct method of terminating an earth cable when you have double insulated fittings?

You can see on the picture I can’t get a wage inside nor a normal connector block it’s just too tight.

I have seen in the past the cpc being bent over and also snipped off which isn’t recommend just wanted to know the correct way of termination.

[ElectriciansForums.net] Double insulated down lights cpc
 
Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
 
Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
Nothing says the whole of the CPC has to form part of a multi core cable.
That wouldn’t be possible even if the termination was within an enclosure.
 
Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
Quite correct but your words are going to deaf ears.
 
Quite correct but your words are going to deaf ears.
I think if anyone has deaf ears, it’s you.
You cite a Regulation which does not apply, then despite me quoting the Regulation which clearly states it does not apply, you then go right back and cite the Regulation again.

Like I said, find a Regulation that requires a CPC that forms part of a multi core cable to have a minimum CSA and find another that requires terminations to be enclosed.
Once you’ve found (or think you’ve found) those Regulations, then explain how they apply to main bonding and earth conductors.
 

Reply to Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top