whats classes as the correct method of terminating an earth cable when you have double insulated fittings?

You can see on the picture I can’t get a wage inside nor a normal connector block it’s just too tight.

I have seen in the past the cpc being bent over and also snipped off which isn’t recommend just wanted to know the correct way of termination.

[ElectriciansForums.net] Double insulated down lights cpc
 
All/most of the LED commercial downlights we fit have drivers that only allow one 0.75mm 2 core flex. Mostly we have plug-in LCM boxes and can wire flex to the plug if it is an MF plasterboard ceiling we use Click-Scholemore flow connectors.
 
It is not permitted for Class 2 items to have an earth connected to them.
I take the view that if you are looping in and out of fittings this is part of the circuit and should have a CPC and that where there is the final connection to a fitting not requiring an earth eg double insulated etc. it is permissible to use two core flex.
 
So does that mean that this class 2 cheap screwfix light does not meet regs as it has made no cpc termination or allowance for terminating cpc within the enclosure.

412.2.3.2 Except where Regulation 412.1.2 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory.


NOTE: This requirement is intended to take account of the replacement by the user of Class ll equipment by Class I equipment.


All depends on how you interpret it.
It doesn't say how it should be "terminated at each point in wiring and at each accessory."
Unusual for the regs not to be clear...... Go figure......
 
So does that mean that this class 2 cheap screwfix light does not meet regs as it has made no cpc termination or allowance for terminating cpc within the enclosure.
Hi - as per Spoon's post it's not clear. I'd say the manufacturer not providing a parking space for the cpc doesn't make it easy for us.
 
As I have already suggested, the solution is to strip the CPC back so that it can be terminated outside of the enclosure.

The minimum CSAs of 2.5mm2 and 4mm2 are not applicable as the CPC forms part of a multi core cable.

There is no requirement in BS7671 for terminations to be made within an enclosure.
However there is a requirement for this CPC to be terminated at the accessory.
 

Reply to Double insulated down lights cpc in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top