J

joehat

For adding an rcd or download grading an mcb for various reasons I've always used a mwc, is this correct or do I need a EIC as this seems alot of work for this?

Sent from my SM-G930F using Tapatalk
 
as you are altering a circuit and not installing a new circuit, a MWC is correct.. come one joe. take the hat off and scratch the brains. this is basic. :30:
 
Last edited:
Interesting question, and I'll be advised by someone with more experience Tel.

My C&G 3292 Course book, suggests replacing a protective device in a non like for like manner, would require an EIC not MWC. Similar answer from Elecsa/NIC technical.

So as I understand things mcb for mcb would be MWC. RCBO for MCB would be EIC. Adding RCD to the circuit origin, would be EIC?
 
But also adding sockets to a circuit only requires a mwc yet it's not like for like, it's changing the circuits characteristics if you think about it?

Sent from my SM-G930F using Tapatalk
 
An alteration or addition needs to be tested and certificated in addition to verifying the circuit is suitable for the alteration before work commences.
132.16, 610.4, and 633.1

How you could argue that changing the OCPD for one with different characteristics is not an alteration I'm not sure.
 
Last edited:
Where in BS7671 is there any mention of the terms 'like for like' or 'characteristics of a circuit'?
What exactly is changing the characteristics of a circuit supposed to signify?

When conducting an EICER, I note that the CPC of an RFC is not continuous.
I find the break in the CPC and make good.
Have I not just changed the characteristics of that circuit?

My 60W incandescent light bulb in my bath room burns out.
I replace it with a 7W CFL.
That's not 'like for like' and the characteristics of the circuit have been altered.
Should it be an EIC or MWEIC?

If it stated in the notes for an MWEIC that it may be used for the 'like for like' replacement for an item of equipment, then fine.
However it doesn't, so please stop introducing terms into the Regulations, which do not exist.
 
Think there's loads of things we should and can't do, that's not in BS7671, (reg 421.1.210 e.g.), that's why 'They' make a fortune out the other publications, that go on to explain the regs and try and make sense of them.

Like the 'Few Good Men' quote, 'Corporal, would you turn to the page in this book (Marine Manual) that says where the mess hall is, please. ........etc etc etc.........'Well, I guess I just followed the crowd at chow time, sir'.
 

Reply to Downgrading mcb or adding rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
4K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top