Hi Guys
I know showers have been extensively covered on here, but this this is a slightly different question.
went to a job to replace 45amp shower switch, I noticed cable was damaged by heat, first thought maybe loose connection, so I started investigating, I noticed a 9.5kw shower on 6.00mm T&E cable enclosed in wall on 40 RCBO, I know without even looking that if it was clipped this might be ok but buried in wall no.
I explained situation to superviser and he was going to ask me to downgrade MCB. I was about to have a debate with him when I found further evidence of severe charring and at that point I said it needs rewiring, IR test showing L/E 0.14 M ohms.
My question is iz>=IN>=IB
downgrading MCB may cover IZ>IN but IB is not covered and my understanding is an MCB will aloow an overload of upto 1.45 times its rating in this case the current carrying capacity of the cable would be 34amps and the fixed load will pull more than this 46.4 for quite some time,thus damaging the cable, am I wrong? if I am in this situation again do I correct him?
thanks in advance for your help
I know showers have been extensively covered on here, but this this is a slightly different question.
went to a job to replace 45amp shower switch, I noticed cable was damaged by heat, first thought maybe loose connection, so I started investigating, I noticed a 9.5kw shower on 6.00mm T&E cable enclosed in wall on 40 RCBO, I know without even looking that if it was clipped this might be ok but buried in wall no.
I explained situation to superviser and he was going to ask me to downgrade MCB. I was about to have a debate with him when I found further evidence of severe charring and at that point I said it needs rewiring, IR test showing L/E 0.14 M ohms.
My question is iz>=IN>=IB
downgrading MCB may cover IZ>IN but IB is not covered and my understanding is an MCB will aloow an overload of upto 1.45 times its rating in this case the current carrying capacity of the cable would be 34amps and the fixed load will pull more than this 46.4 for quite some time,thus damaging the cable, am I wrong? if I am in this situation again do I correct him?
thanks in advance for your help