dinger809

-
Arms
Joined
Dec 5, 2014
Messages
104
Reaction score
147
Location
Essex
Hello chaps
I have been to a house today, which has (I feel) far too many downlights per room. The lounge for example has 29 downlights in an area measuring 12.5 feet by 22feet (about 4 x 7 metres for the youngsters). The lights are split into three lots, so no problem with loading. My question is, does anybody have or aware of an actual formula to work out the number of these things for a room area. I've been looking, but can't find anything. Many thanks
 
Relux or Dialux are Lighting calculation programmes, but you will require an IES or LDT file for either the fitting or the lamp.
This program is used for mainly commercial and industrial lighting but it will do domestic providing you can get hold of the above mentioned files .
The software is available as a free download, but it may not be easy to use at 1st , I use it for all my Lighting designs and client gets the design to sign off prior to install.
Hope this helps you
 
29 does sound a lot for that space, could likely get away with around half that number.

There is quite a variation in lumen output of different brands and their ranges, not to mention beam angles and height of ceiling that also come into play. I normally opt for around 550-700mm from walls, and between 900-1200mm spacing between each fitting.
 
Generally you would as a starting point be looking at a spacing of about 3ft apart for standard downlights.
This is a possible method of calculation that I obtained somewhere on an earlier web trawl:
Lighting Calculations
How Many Fittings are Required for a Room
The utilisation factor table and a few simple formulas allow us to calculate the number of fittings required for any room.
Utilisation factor table that is available on most fittings.
e.g. UTILISATION FACTOR TABLE (for 2x36 bare batten)
LOR: 88.1% SHR NOM 1.75: 1.0 Disregard SHR MAX.
Reflectance Room Index (K)
Ceiling Wall Floor 0.75 1.00 1.25 1.5 2.0 2.50 3.00 4.00 5.00
0.50 0.30 0.20 0.30 0.37 0.42 0.46 0.52 0.56 0.59 0.63 0.66
Across the Top of the Table
Name Description
LOR Light output ratio for this fitting. Not required in a simple calculation.
SHR NOM Nominal Spacing to Height ratio. For a given mounting height we can see the nominal spacing between fittings. E.g. 1.75 to 1 means that for every 1 metre of mounting height (above work plane) we should have a maximum 1.75 metres between fittings.
SHR MAX Used by lighting design software and not needed for manual calculations.
Reflectance Select a horizontal line for the reflectance values that best describe the room.
Typical Reflectance Values are:
Ceiling Walls Floor
Air Conditioned Office 0.7 0.5 0.2
Industrial 0.5 0.3 0.2
Utilisation Factor (body of the table)
This is a value between 0 and 1 that represents the percentage of total lamp lumens in the room that fall on the work plane. It takes into account the room reflectances, room shape, polar distribution and light output ratio of the fitting.
Step 2: Calculate Room Index (K)
Room Index:
The room index is a number that describes the ratios of the rooms length, width and height.
Formula: K = (L x W)/ (Hm (L+W))
Where: L = Room Length, W = Room Width, Hm = Mounting Height of Fitting (from working plane), Work Plane = Desk or Bench Height
The result of this calculation will be a number usually between 0.75 and 5.
Note: This formula for K is only valid when room length is less than 4 times the width or when the K value is greater than 0.75.
Step 3: Using the room index and reflectance values in the utilisation factor table
For the horizontal row select the reflectance that best describes the room.
For the vertical column select the room index value K as calculated above.
The utilisation factor for this fitting in this room is where the row and column intersect.
Step 4: To calculate the number of fittings required use the following formula:
Formula: N = (E x A)/(F x uF x LLF)
Where:
N = Number of Fittings, E = Lux Level Required on Working Plane , A = Area of Room (L x W), F = Total Flux (Lumens) from all the Lamps in one Fitting, UF = Utilisation Factor from the Table for the Fitting to be Used, LLF = Light Loss Factor. This takes account of the depreciation over time of lamp output and dirt accumulation on the fitting and walls of the building.
Typical LLF Values
Air Conditioned Office 0.8
Clean Industrial 0.7
Dirty Industrial 0.6
Step 5: Space the number of fittings uniformly around the room drawing and check the SHR nominal for the fitting has not been exceeded. If it has been exceeded re space the fittings to get back to SHR nom.
Step 6: Work out the number of fittings required in each axis of the room:
Number in Length = Root (Total * L/W)
Number in Width = Root (Total * W/L)
 
about 800 mm from the walls , and no further apart than 1400 mm - in a standard height room

Another relevant thing to consider is how good are the wall finishes. If they are rough as a badgers .... then 800mm from the walls is defo preferable to 600mm which would highlight every bump and defect on the wall.

Richard: I know you give some cracking answers to questions and queries but please tell me you copied and pasted that lot!! :dizzy:
 
Another relevant thing to consider is how good are the wall finishes. If they are rough as a badgers .... then 800mm from the walls is defo preferable to 600mm which would highlight every bump and defect on the wall.

Richard: I know you give some cracking answers to questions and queries but please tell me you copied and pasted that lot!! :dizzy:

No, I just thought about it a bit, researched the available information on light fittings and room construction and devised a method of calculation and jotted it down here for the OP!:innocent:

or possibly "This is a possible method of calculation that I obtained somewhere on an earlier web trawl:":grinning:
 
Relux or Dialux are Lighting calculation programmes, but you will require an IES or LDT file for either the fitting or the lamp.
This program is used for mainly commercial and industrial lighting but it will do domestic providing you can get hold of the above mentioned files .
The software is available as a free download, but it may not be easy to use at 1st , I use it for all my Lighting designs and client gets the design to sign off prior to install.
Hope this helps you

I would have been happy fitting 6 or 8 with a 60 degree beam angle . 6 would give 5100 lumens with an 850 lumen fitting . plenty of light for a living room . warm white on a dimmer .
 

Reply to Downlight Installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
After fitting out the first room of downlights.... i expect him to get a bit speedier at fitting them There is so many unknowns to price at this...
2
Replies
25
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
885

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top