I will try to explain this as best as I can,
Wired 18 downlights in two rows of 9,
The downlights were wired in 3core and earth cable so two switch wires could be used to switch the downlights however the customer wished. It was opted for the lights to be switched in banks of two on alternating switch wires (hope that makes sense)
So the problem is ALL the lights turn on regardless of which switch wire is on (with the other off) The lights do seem slightly dimmer on the switch wire that remain off.
The downlights used are cheap LAP LED fittings bought by the customer,
The run is quite long from the switch to the last fitting.
I/R between switch wires >200M
47V coming back on switch wire that is off when other switch wire is on voltage decreased to 25v when half the downlights were disconnected.
Any help?
I'm thinking potentially induced voltage from 3core? would installing different fittings remedy the situation?
Thanks
 
Induced voltage from 3 core is highly unlikely I would have thought as this method is used for all manner of lights including emergency fittings without issue. If you are absolutley certain the Cabling has no faults and your connections are correct I would remove the fittings and see if the voltage still appears on the other core.
 
Exactly, remove lamps and try with an old halogen bulb , if that don't work remove lamps and test voltage between phases and N on the cable with a good volt meter.
 
I think a break somewhere on the neutral might cause this problem.

You have 3 conductors L1, L2 and N.
Say L1 is switched on 230V, L2 switched off.
Lamps on L1, upstream of the break in the N will complete the circuit normally
Lamps on L1 downstream of the break in the N will complete the circuit like this:
  • through L1
  • through lamp(s) on L1 downstream of the N break
  • through the N downstream of the break
  • through lamp(s) on L2 downstream of the N break via their N
  • through L2
  • through lamp(s) on L2 upstream of the N break
  • through N upstream of break to CU
So all lamps on L2 will see some voltage
 
I drew the diagram out for this so I could understand it easier and yes its definitely likely as the neutrals on the fittings aren't hard fixed and are magically looped somewhere under the cover of the fitting, just trying to think of the best way to test this theory?
Disconnect all fittings from one of the strings and temporarly link them and if there is a neutral break down no lights will illuminate??
I think a break somewhere on the neutral might cause this problem.

You have 3 conductors L1, L2 and N.
Say L1 is switched on 230V, L2 switched off.
Lamps on L1, upstream of the break in the N will complete the circuit normally
Lamps on L1 downstream of the break in the N will complete the circuit like this:
  • through L1
  • through lamp(s) on L1 downstream of the N break
  • through the N downstream of the break
  • through lamp(s) on L2 downstream of the N break via their N
  • through L2
  • through lamp(s) on L2 upstream of the N break
  • through N upstream of break to CU
So all lamps on L2 will see some voltage
 
I drew the diagram out for this so I could understand it easier and yes its definitely likely as the neutrals on the fittings aren't hard fixed and are magically looped somewhere under the cover of the fitting, just trying to think of the best way to test this theory?
Disconnect all fittings from one of the strings and temporarly link them and if there is a neutral break down no lights will illuminate??
If I've understood you correctly, the lights upstream of the break will still come on, but downstream would not illuminate.

You wired this yourself, so you know the route the cable takes? You might be able to pick up the break with your volt stick, depending on its range, without disconnecting anything.

Live test, 1 switch on, the other off.

At the supply end of the 3 core cable, the neutral will be at about 0V to earth, so should give no indication on your volt stick. After the break, it will be somewhat above earth voltage, so may well light up the volt stick.

So start at the supply end, testing the neutrals as you go out, until you find the first neutral that lights up. If it doesn't work, turn the switch off, and the other on, and try again.
 

Reply to --------Downlighter fault!!--------- in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
I'd start by doing the usual supply impedance tests followed by N-E voltage with the installation under some load. Also visually inspect and...
Replies
4
Views
1K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
677
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top