Was it a true ZE test? - (did you remove parallel paths before test?)

If that was a clean ZE reading then you have a poor L - E loop (loose connections dodgy cable etc etc)

Again also you could be getting parallel path on your ZS and the cpc not connected at all.

I assume you did r1 + r2 dead test?
 
It may sound stupid but did you check the connections from MET (if there is a seperate MET) to the CU earth bar?

If it is on every circuit you are getting a breakdown some where between MET and CU

Do you have any pics of the earthing arrangements/connections.
 
it is a tns system and i tested at the db on just the main earth and the sheath of the supply and reading was the same 0.75ohm. the only odd thing about it was there was some damage to the sheath of the supply and the original earth clamp had signs of arcing perhaps a previous fault and a loose clamp but still came up with a ok reading with a new clamp.

asked several electricians i used to work with and non of them could give me answer as what could be causing the high reading.
 
Zs = ( R1+R2) + Ze. as truckster said, could be RCDs/MCBs cocking it up. try taking a Zs reading on the busbars. if that is ridiculously high, you know it's not a problem with the circuits.
 
cheers for that amazing what you forget from you college days such a simple calculation and could i hell think how to do it.

yea il give that a go hopefully that will be all it is, on another note have any of you ever seen damage to the main earth clamp/sheath before from arcing?
 
If you've forgotten such a simple calc what sort of electrical work do you normally do?

As your post indicates you don't normally do domestic work, dare I mention notification to BC & Part P (on the basis you're in E&W)?
 
i assume he means england and wales. part p does not apply in scotland, southern ireland, outer mongolia, kazeckstan, '''''''''''''''
 
I'd test on each side of the rcds to see what if any the difference is. Also your saying that every circuit is around 114 ohms?

Is your tester working properly, as every domestic job i've done, measured Zs values differ quite a bit between say a lighting circuit and a shower or cooker radial
 

Reply to Earh loop problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
529
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
758
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top