yes telectrix is correct i am currently doing the 2394 course and the teacher is not that great one time i asked him about N & E combined as i couldnt get my head around it and his answer was neither could he .
Its easy. TNS, Earth Neutral Separated. TNCS, Earth Neutral Combined and Seperated.
The first thing that you need to know and understand, is that the Neutral and Earth are NEVER combined in the installation and it is not allowed. If you look in the OSG or GN3 you will see from the illustrations that TT, TNS and TNCS are identical on the consumer side of the illustration.
Therefore when we refer to Neutral and Earth combined it is on the SUPPLY side only.
TNS, this system provides a two core supply cable to the cutout fuse (Supply head), and the main earthing conductor is connected to the metal sheath of the supply cable, so you have 3 seperate connections back at the supply transformer, Line Neutral and Earth.
TNCS, this system provides a split concentric cable (it looks like a single core SWA cable if you cut through it..dont!) to the supply head, The core is used as the Line, the steel armouring is connected to the Neutral at the supply head, and the main earthing conductor goes into and connects to the Neutral in the supply head from either an adjacent earth block or the earth bar in the CU. Therefore there is only one combined connection for the Earth and Neutral from the supply head to the supply transformer. In some cases the distributor will fit additional earth rods to the split concentric cable to ensure that the Ze stays in spec. TNCS is sometimes referred to as "PME" protected multiple earthing.
Cheers..............Howard