44ALLAN
You were right with the 22kΩ Tel-there's another 1000Ω allowed in the equation for the resistance of a human body
What happens if your voltage is 246 tho !
Be more than 10mA using them numbers
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss earth bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
You were right with the 22kΩ Tel-there's another 1000Ω allowed in the equation for the resistance of a human body
You were right with the 22kΩ Tel-there's another 1000Ω allowed in the equation for the resistance of a human body
What happens if your voltage is 246 tho !
Be more than 10mA using them numbers
10.69ma
.TNCS, this system provides a split concentric cable (it looks like a single core SWA cable if you cut through it..dont!) to the supply head, The core is used as the Line, the steel armouring is connected to the Neutral at the supply head, and the main earthing conductor goes into and connects to the Neutral in the supply head from either an adjacent earth block or the earth bar in the CU. Therefore there is only one combined connection for the Earth and Neutral from the supply head to the supply transformer. In some cases the distributor will fit additional earth rods to the split concentric cable to ensure that the Ze stays in spec. TNCS is sometimes referred to as "PME" protected multiple earthing
Just looked at the split concentric photo link not keen on using a red conductor on the neutral.
That's meter fitters for you!! lol!! Probably only had red tails in the van, or as is not too uncommon these days got his polarity wrong!! lol
yeah...i keep tryin to drive this message home in here Allan...And earthing and bonding are two different things
Reply to earth bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net