Hi All , I am new to this forum but am an industrial electrician (20 years) but have been using my Robin KTS1620 Multi tester in my house to do a few tests as i am considering returning to partp work as my industrial work is quiet.
The house is supplied by a TT System through a 100mA RCD.
I connected my tester to the ring circuit and found the earth fault loop impedance to be 40 ohms and the prospective short circuit current to be only about 5 Amps !. I decided to investigate the earth and found the earth spike to be buried near to the road. I disconnected the lead from the main earthing terminal that goes to the earth rod but cannot get an earth loop impedance reading through the rod ? Does this mean the rod is failing to connect to earth , if so am i right in assuming the 40 ohm reading must be got through the gas / water pipe bonding ?
Also i assume i should now be fitting a 30 mA RCD in series with the 100mA RCD for greater protection ?
Any help appreciated
Chris
The house is supplied by a TT System through a 100mA RCD.
I connected my tester to the ring circuit and found the earth fault loop impedance to be 40 ohms and the prospective short circuit current to be only about 5 Amps !. I decided to investigate the earth and found the earth spike to be buried near to the road. I disconnected the lead from the main earthing terminal that goes to the earth rod but cannot get an earth loop impedance reading through the rod ? Does this mean the rod is failing to connect to earth , if so am i right in assuming the 40 ohm reading must be got through the gas / water pipe bonding ?
Also i assume i should now be fitting a 30 mA RCD in series with the 100mA RCD for greater protection ?
Any help appreciated