Hi all,

Hope you are all well and all is good!

I am installing a sub board being fed by a 80A SP+N Metal Switch Fuse at source, this is feeding a 25mm 3 core SWA at a length of about 2 meters to the main DB (both boards are metal). I am being challenged in saying that I have to add an earth fly lead at both ends, preferably the same size as the CPC e.g. 25mm, as the glands will be fine for continuity of CPC into the armour.

Am I being super safe or just a moron, whats the right answer?

Thanks all.
 
i would add fly leads to ensure that the steel armour is reliably earthed. seen a couple of sites where the continuity from earth bar to metal casing is poor. if you do the adiabatic, bearing in mind the restivity of the armour, 10mm should suffice.
 
i would add fly leads to ensure that the steel armour is reliably earthed. seen a couple of sites where the continuity from earth bar to metal casing is poor. if you do the adiabatic, bearing in mind the restivity of the armour, 10mm should suffice.
Thanks Telectric, my thoughts exactly, but was just going to be over kill with the fly lead.
 
Are you talking about leads from the glands' banjo (or better still Earthing nut / Piranha nut) to the related earth terminals?

Yes, you should do it as you can't always be sure the box will be in great contact, not corrode a bit with time, or even (probably not here) be able to cope with the fault currents.

  • Simple answer is to go with the CSA from Table 54.7 in the regs, which in your case is 16mm.
  • Or you can go with the adiabatic calculation, and the fastest way to check that would be Table B4 from the OSG which should no change in Zs 0f 0.4 ohms from from 10mm to 16mm, implying 10mm is fully OK for a 80A fuse and 5s disconnection times.
  • Also you also really should consider the limits of Table 54.8 for the TN-C-S case in case there is extraneous stuff bonded to the CU earths, which typically means a 10mm minimum.

TL;DR Use 10mm or 16mm as you have lying around in this case!
 
Just looked over again and realised you have a CPC in the 3 cores of the SWA, that takes away the issue of TN-C-S bonding as you already have the sizeable end-end path.

However, you should still be designing to cope with an internal cable fault/penetration incident even if very unlikely, and so you should have the armour ends rated for fault-clearing of the 80A fuse.

You could get away with just 10mm at the only feed end, but I would say it is still good practice to have both ends able to cope with any fault currents. In reality 6mm at both ends should be sufficient, but 10mm would be meeting all requirements without assumptions of current sharing, etc.
 

Reply to Earth fly lead size & requirement in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
638
loz2754
L
Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top