Good evening all, Happy Weekend
Just thought I'd post another thread as I have given my earth leakage clamp meter an outing today and need to learn a little more about the results I am receiving.
Firstly, 16th Edition board - RCD - Shower, Cooker, Sockets, Sockets, Sockets and then two lighting circuits on the unprotected side.
Called to a job because everytime they turn on the shower the RCD trips. No loose terminals in entire board or shower unit. Checked the isolator switch to find that one of the terminals on the neutral had a snapped screw. This could be undone with long nose pliars and the copper had turned an almost silver colour so I thought I was onto a solution. I replaced the switch with a new MK type after I had IR'd on a 250 and 500v test, both supply and load cable came back with maximum readings. Refitted everything ensuring all connections were tight and fired up shower again.
The shower pulls 34.6 amps on a 40A breaker.
On packing up my tools and after running shower for approx 20 minutes, TRIP! Damn, wasn't that then lol
Clamped my earth leakage meter onto the shower circuit cpc and obtained very high readings, high as in exceeding 30mA high on one instance.
Now, I have left the circuit isolated because like I explained to the client I could remain there for the rest of the day testing and looking for faults BUT all it will do mostly is rack up the hourly charges and I still believe the fault is related to the shower.
When clamping the main earth even with the shower running I couldn't get a reading over 10mA (100A main fuse)
The shower is now running for much longer as originally it would trip everything immediately before (although it did not trip immediately on arrival).
My thoughts are that I could move this shower circuit onto an unprotected way and use a 40A RCBO thus reducing issues with the rest of the property being affected if the circuit trips. Can anyone say that they see any concerns with this proposal giving the high earth leakage that was detected? I've read that an installation should not exceed 10mA earth leakage if protected with 100A fuse, can anyone shed any light on this matter that will aid me making a decision? It's too easy to say your shower has had it you need to spend a couple of hundred quid to swap it when swapping in a 20 quid RCBO may resolve the issue or at least make the installation far safer.
What would be the maximum earth leakage you would expect to see on something like this? I have seen that a cooker max should be approx 5mA?
It's great having these fancy bits of kit but useless if you cannot read the results correctly.
Any assistance would be much appreciated, it would also be great if someone could point me to some literature that would benefit me as I want to understand this issue.
This is an ongoing fault finding exercise, which is why the shower remains isolated to try and eliminate/prove the where the fault is without running up too much expense in labour.
Kind Regards
1SC
Just thought I'd post another thread as I have given my earth leakage clamp meter an outing today and need to learn a little more about the results I am receiving.
Firstly, 16th Edition board - RCD - Shower, Cooker, Sockets, Sockets, Sockets and then two lighting circuits on the unprotected side.
Called to a job because everytime they turn on the shower the RCD trips. No loose terminals in entire board or shower unit. Checked the isolator switch to find that one of the terminals on the neutral had a snapped screw. This could be undone with long nose pliars and the copper had turned an almost silver colour so I thought I was onto a solution. I replaced the switch with a new MK type after I had IR'd on a 250 and 500v test, both supply and load cable came back with maximum readings. Refitted everything ensuring all connections were tight and fired up shower again.
The shower pulls 34.6 amps on a 40A breaker.
On packing up my tools and after running shower for approx 20 minutes, TRIP! Damn, wasn't that then lol
Clamped my earth leakage meter onto the shower circuit cpc and obtained very high readings, high as in exceeding 30mA high on one instance.
Now, I have left the circuit isolated because like I explained to the client I could remain there for the rest of the day testing and looking for faults BUT all it will do mostly is rack up the hourly charges and I still believe the fault is related to the shower.
When clamping the main earth even with the shower running I couldn't get a reading over 10mA (100A main fuse)
The shower is now running for much longer as originally it would trip everything immediately before (although it did not trip immediately on arrival).
My thoughts are that I could move this shower circuit onto an unprotected way and use a 40A RCBO thus reducing issues with the rest of the property being affected if the circuit trips. Can anyone say that they see any concerns with this proposal giving the high earth leakage that was detected? I've read that an installation should not exceed 10mA earth leakage if protected with 100A fuse, can anyone shed any light on this matter that will aid me making a decision? It's too easy to say your shower has had it you need to spend a couple of hundred quid to swap it when swapping in a 20 quid RCBO may resolve the issue or at least make the installation far safer.
What would be the maximum earth leakage you would expect to see on something like this? I have seen that a cooker max should be approx 5mA?
It's great having these fancy bits of kit but useless if you cannot read the results correctly.
Any assistance would be much appreciated, it would also be great if someone could point me to some literature that would benefit me as I want to understand this issue.
This is an ongoing fault finding exercise, which is why the shower remains isolated to try and eliminate/prove the where the fault is without running up too much expense in labour.
Kind Regards
1SC