Bang on....what I've been trying to get E54 to see for ages:D......For that reason IMO there is little point in going to excessive lengths to achieve very low Ra's,which cant ever be relied upon to be stable enough for operation of all the overcurrent devices in an installation.

The point is, that i've always stated that a TT system for a domestic installation should always avoided and be a last choice not a first choice!!! If your stuck with a TT system, then that's another matter altogether. Then you do the job properly and wherever possible use deep driven rods of a decent diameter!! Depending on the soil type it is more than feasible to get an Ra far lower than 10 ohms and the deeper you go, ...the more stable the system will become. The common use of these thin short earth rods, ....and then only using ''one'' of them, is the main reason why it is so hard to get anywhere near a decent Ra value, an that's the real truth of the matter...

These lattice mats that have been mentioned above, are Not going to be anywhere near stable if buried at one metre or less, in fact there primary use is for rocky locations or where you can't drill or drive rods to any depth....
 
Im going to install a screw joined one (2 of) when I get the chance as the one I did went in a bit easy for my liking even though the Ra droped considerably from the old one
 
Last edited by a moderator:
The deeper the better Cider, and if your only using 1.2M rods, then consider one more making 3.6m. ...Remember, that first metre of depth will be giving you nothing, during winters freezing weather conditions!!!!
 
I got a rod down to 1ohm before, at the side of a road in the centre of london. About 3 lots of 8 5/8 rods. Used a kango though.

True story.
 
I got a rod down to 1ohm before, at the side of a road in the centre of london. About 3 lots of 8 5/8 rods. Used a kango though
True story.

Glad to see, that there are still those that are prepared to do a decent job of creating a good TT system. Sounds like you missed the predominant London clay, you wouldn't have had to use anywhere near as many rods!! ...lol!!

I wouldn't be a bit surprised that if you went back and retested that TT system, one to three years later, you would find your Ra will be well within the ''sub'' 1 ohm value!!! As most deep driven rod values, improve over the first few years....

A kango or similar purpose made mechanical hammer, is the only sensible way to deep drive rods past 3 metres...
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earth rod distance to gas service
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Cider,
Last reply from
Engineer54,
Replies
24
Views
9,160

Advert

Back
Top