Bang on....what I've been trying to get E54 to see for ages:D......For that reason IMO there is little point in going to excessive lengths to achieve very low Ra's,which cant ever be relied upon to be stable enough for operation of all the overcurrent devices in an installation.

The point is, that i've always stated that a TT system for a domestic installation should always avoided and be a last choice not a first choice!!! If your stuck with a TT system, then that's another matter altogether. Then you do the job properly and wherever possible use deep driven rods of a decent diameter!! Depending on the soil type it is more than feasible to get an Ra far lower than 10 ohms and the deeper you go, ...the more stable the system will become. The common use of these thin short earth rods, ....and then only using ''one'' of them, is the main reason why it is so hard to get anywhere near a decent Ra value, an that's the real truth of the matter...

These lattice mats that have been mentioned above, are Not going to be anywhere near stable if buried at one metre or less, in fact there primary use is for rocky locations or where you can't drill or drive rods to any depth....
 
Im going to install a screw joined one (2 of) when I get the chance as the one I did went in a bit easy for my liking even though the Ra droped considerably from the old one
 
Last edited by a moderator:
The deeper the better Cider, and if your only using 1.2M rods, then consider one more making 3.6m. ...Remember, that first metre of depth will be giving you nothing, during winters freezing weather conditions!!!!
 
I got a rod down to 1ohm before, at the side of a road in the centre of london. About 3 lots of 8 5/8 rods. Used a kango though.

True story.
 
I got a rod down to 1ohm before, at the side of a road in the centre of london. About 3 lots of 8 5/8 rods. Used a kango though.

True story.

Miles of gas and water pipes make great fault paths when you've hit a few of them don't they! ;) :rofl:
 
I got a rod down to 1ohm before, at the side of a road in the centre of london. About 3 lots of 8 5/8 rods. Used a kango though
True story.

Glad to see, that there are still those that are prepared to do a decent job of creating a good TT system. Sounds like you missed the predominant London clay, you wouldn't have had to use anywhere near as many rods!! ...lol!!

I wouldn't be a bit surprised that if you went back and retested that TT system, one to three years later, you would find your Ra will be well within the ''sub'' 1 ohm value!!! As most deep driven rod values, improve over the first few years....

A kango or similar purpose made mechanical hammer, is the only sensible way to deep drive rods past 3 metres...
 

Reply to Earth rod distance to gas service in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
814
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
988

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
3K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top