should you install a earth rod if running a feed to a shed which is built on timber frame and is all timber , no metal parts and will have no services ie gas or water in it so no need for bonding only a supply for a light and a couple of sockets or can you use a pme earth from fuseboard if the shed supply is run in 6mm armoured from the outside of the house ( inside house 6mm t+e to fuseboard ) protected by 32amp rcbo will be installing a 2 way board with rcd main switch in shed approx 25 meters away
 
What scheme is that? Whenever I rung Elecsa tech helpline, they never asked me anything to verify membership.
Stroma
As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
I’m running swa outside from the house to shed terminating into a wiska box then t+e in cupboard in trunking up to ceiling then will be clipped in ceiling void , before dropping back down to fuseboard which is cupboard under the stairs client doesn’t want any chasing
 
Stroma

I’m running swa outside from the house to shed terminating into a wiska box then t+e in cupboard in trunking up to ceiling then will be clipped in ceiling void , before dropping back down to fuseboard which is cupboard under the stairs client doesn’t want any chasing
Sorry yes just read post 10 .no nead for the upfront Rcd then and with no extraneous conductive part i cant see a problem using the pme
 
The 2 RCDs in series will still work but it's best avoided. Often both will trip on a fault, or when you're trying to test. On the plus, it will allow you the opportunity to show how to test each separately if you want :) .
 
Just a note as the title is somewhat ambiguous, the PME arrangement stops at the cutout, we do not export or extend PME normally as that would need to be agreed with the National Grid guys, I sense you didn't mean this, the PME or other arrangement at source can effect though your own earthing arrangments which will be a TNS format or a TT or a mixture.
If you ever have a PME or TNCS at source then you have a very sound reliable earthing system and regardless how the outbuilding is arranged I would always use the provided earth and if needed then bring an equipotential bond out... I would only consider TTing the out building to reduce costs on a bigger scale but there would need to be a very large distance to be covered to justify this IMHO. TT systems are inherently variable so getting a constant reliable good earthing reading is difficult as your readings are easily effected by the conditions on the day.
 
Just a note as the title is somewhat ambiguous, the PME arrangement stops at the cutout, we do not export or extend PME normally as that would need to be agreed with the National Grid guys, I sense you didn't mean this, the PME or other arrangement at source can effect though your own earthing arrangments which will be a TNS format or a TT or a mixture.
If you ever have a PME or TNCS at source then you have a very sound reliable earthing system and regardless how the outbuilding is arranged I would always use the provided earth and if needed then bring an equipotential bond out... I would only consider TTing the out building to reduce costs on a bigger scale but there would need to be a very large distance to be covered to justify this IMHO. TT systems are inherently variable so getting a constant reliable good earthing reading is difficult as your readings are easily effected by the conditions on the day.

There are a few situations when utilising the PME earthing arrangement on installations outside of the EBZ is not permitted due to safety, not cost.

For example is it was a metal outbuilding then it would almost be a certainty that an earth electrode would have to be used. Building sites is another example.
 
I would like to see a reference for your 'not permitted' claim, I haven't worked on building sites for over 20yrs so maybe a bit out of touch and will happily stand corrected.
I agree that it may be easier to TT on a building site but we are taking my comment a little out of context, we are discussing a permanent install here not a temp', the cost issue is the opposite if it is temp' and there in my mind is no other reason than reducing costs as to why you cannot bond the metal outbuilding as would be done in a permanent install other that running a separate earthing conductor may leave it vulnerable to damage if say the other cables are SWA.
 
I would like to see a reference for your 'not permitted' claim, I haven't worked on building sites for over 20yrs so maybe a bit out of touch and will happily stand corrected.
I agree that it may be easier to TT on a building site but we are taking my comment a little out of context, we are discussing a permanent install here not a temp', the cost issue is the opposite if it is temp' and there in my mind is no other reason than reducing costs as to why you cannot bond the metal outbuilding as would be done in a permanent install other that running a separate earthing conductor may leave it vulnerable to damage if say the other cables are SWA.

There is no dispensation in the Regs for temp install. All installs regardless of their length of service need to meet BS7671 in full.

I will open the BBB sometime this morning and have a look.

The reason we do not use a PME for a metallic outbuilding is if a PEN conductor fails on the DNO side it will bring the neutral, and therefor the earth in the installation up to 230 volts. I would not fancy opening the door to the metal outbuilding while standing on the grass would you?
 
Let's just word this correctly, we are not using PME or suggesting it for the outbuilding which was the initial point in my post, we are extending the EBZ where the incoming supply is PME (noted you did say about EBZ earlier)
Also PEN conductors in a PME setup have multiple points of earthing along their length to protect against such network faults, it is TNCS that has an increased risk of ground faults but if bonded correctly then on these rare events the risks are minimised.

What can occur though is a PD between supplied earth and actually ground if you are in an isolated metal framed building where you could touch it and bridge between true ground and supplied earth, in these cases where the structural is exposed metal and it is raised up on something insulating where TT is not used then I have in the past implemented a dual arrangement of extending the BZ and adding Earthing rods. The strange thing is the BS7671 or guidance does not cover this latter scenario although it is a very real example and does pose a risk even from small network leakage through damaged cables of mainly the older kind where any steel ducting, armouring etc has corroded over time.

PS - if it is in guidance notes then this at most is just a simplified guide for most situations and often uses a hammer to crack a nut approach.
 
Last edited by a moderator:

Reply to Earth rod needed for shed supply or pme allowed ???? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
712
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top