@essex
'You keep saying about wording it correctly but throughout 7671 it is worded as using the PME earthing facility.'
It is worded correctly in the BS7671.. the PME earthing facility is the incoming earth/neutral connection into the cutout, after that its is no longer classed as PME and changes to normally TNS or TT, so when people talk about taking PME out to a shed this is a very different thing and would mean you are keeping the combine N/E set upwhich would require special permissions.
'
As for where the PEN conductor is earthed, it is impossible to determine either if it is earthed, where it is earthed, how effective the earth is and also where the fault is on the PEN conductor. As such it is completely pointless bringing this up. It brings nothing to the design process.'
The debate is regarding a PME supply which will likely have a PEN conductor, been PME then it does have multiple earthing grounding straps/rods along the supply cable length so it is a valid point to bring it up as we were discussing the need to TT a metal cabin on a building site and I provided my opinion why this cannot be based on a PME system when you describe a damaged cable.
Regulation 717.411.4 - this is in agreement with everything I have said so far.
'
I would be really interested in how you extended an EBZ but also determined that you needed earth electrodes??'
It was done on a stone yard site where they used steel shipping containers for a canteen and locker rooms, these were sat on railway sleepers just to avoid them corroding in the mud and had a step to the metal door of the cabin, it was simple to touch the container while been on the true ground, I initially just extended the EBZ as this was a reliable earthing source but comments of occasional tingles came back, now I tested it all and inspected with a fine tooth brush, rcd's operated etc etc couldn't find anything until I got called out in the rain and found they were touching the cabin outside while on true ground, it turns out there was about 55v PD between the wet ground and earthed cabin... Instinct would have been to remove the EBZ at entry and rod it but we had other earthed equipment and pipes within close proximity so it was decided to do a combination.
The leakage couldn't be identified as part of any of the installation and the Supplier says they couldn't identify any issues on their system but said it may not show up or could be a remote issue in someones else's property.
In such scenarios now I tend to belt and brace regardless as it is clear the BS7671 doesn't account for all circumstances hence it is only a guidance.
This particular subject has been discussed at length on the forum numerous occasions, the one I see on the internet the most but not on here too much is garden hot-tubs where people are getting shocks when climbing in or out of the spar, they are fully earthed and rcd functions are fine.. it too comes down to a PD between the supply earth and the actual ground from a possible local fault be it grid or dodgy garden electrics possible even a neighbours, in such cases the advice is the same as well as trying to identify the fault which isn't always possible.