Had to install a earth Rod in rural area today because the Ze on the current TN-S system was too high.
All the circuits are brand new, but for some reason a circuit with LED Haler downslight on seem to trip when the systems earth is changed to the earth rod. The Ze of the system is 11.1ohms.
Every other circuit is fine.

2nd Question:
As my Ze is higher, all the readings im getting for my Zs are too high, but would i be right in thinking they circuits meet the disconnection times because of the RCD, so the high Zs does not matter?
 
Being stupid, as their was no main earth bonds connected thought it would be ok.

Have not been able to test inside the house yet as owner are away till next week, but i have had major issues with DNO lately and Ze being too high and they will not do anything about it as they say they do not maintain the earth?
 
because if it is and the DNOs equipment is already being used as the means of earthing to this property ..clearly it is (TN-S)....then they have a duty of care to maintain this arrangement......
 
because if it is and the DNOs equipment is already being used as the means of earthing to this property ..clearly it is (TN-S)....then they have a duty of care to maintain this arrangement......

I have had 2 flats i tested in london in the past 2 months where DNO will not sort out high Ze. Has been a nightmare!
 

Reply to Earth rod, RCD tripping fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
382
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
486

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top