J

Jel

1st question:
Had to install a earth Rod in rural area today because the Ze on the current TN-S system was too high.
All the circuits are brand new, but for some reason a circuit with LED Haler downslight on seem to trip when the systems earth is changed to the earth rod. The Ze of the system is 11.1ohms.
Every other circuit is fine.

2nd Question:
As my Ze is higher, all the readings im getting for my Zs are too high, but would i be right in thinking they circuits meet the disconnection times because of the RCD, so the high Zs does not matter?
 
because if it is and the DNOs equipment is already being used as the means of earthing to this property ..clearly it is (TN-S)....then they have a duty of care to maintain this arrangement......
 
because if it is and the DNOs equipment is already being used as the means of earthing to this property ..clearly it is (TN-S)....then they have a duty of care to maintain this arrangement......

I have had 2 flats i tested in london in the past 2 months where DNO will not sort out high Ze. Has been a nightmare!
 
My heads sort of spinning here!!! What have you connected the SWA (earthing) of this cable too, at the origin in the house and how have you connected it?? I take it you have glanded both ends??

I really don't know why you have rodded this out building, if the DNO provided earthing point is not functioning at a suitable protection level, they are duty bound to maintain it, even if it means PME'ing the supply if it's available...

Your earth rod(s) will come in handy then, as a locally installed part of the multiple earthing arrangement!! lol!!!
 
With the greatest respect, trying to get experience by playing with an earthing system is not the best idea. Better to get professional help here.
Also, 25mm swa for an outbuilding is probably excessive...
 
My heads sort of spinning here!!! What have you connected the SWA (earthing) of this cable too, at the origin in the house and how have you connected it?? I take it you have glanded both ends??

I really don't know why you have rodded this out building, if the DNO provided earthing point is not functioning at a suitable protection level, they are duty bound to maintain it, even if it means PME'ing the supply if it's available...

Your earth rod(s) will come in handy then, as a locally installed part of the multiple earthing arrangement!! lol!!!
well this is what i was getting at a bit earlier in this thread eng......DNOs dodgin out of their responsibilities again.....keeps surfacing this one doesn`t it?!!....
 

Reply to Earth rod, RCD tripping fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok I’ll try this when I’m down
Replies
4
Views
285
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
357
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
608
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
558
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
446
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks