1st question:
Had to install a earth Rod in rural area today because the Ze on the current TN-S system was too high.
All the circuits are brand new, but for some reason a circuit with LED Haler downslight on seem to trip when the systems earth is changed to the earth rod. The Ze of the system is 11.1ohms.
Every other circuit is fine.
2nd Question:
As my Ze is higher, all the readings im getting for my Zs are too high, but would i be right in thinking they circuits meet the disconnection times because of the RCD, so the high Zs does not matter?