Hi, my first post so be gentle.
Got my MCS inspection on the 24th March and I'm struggling with earthing the array frame.
I have installed an SMA 4000tl inverter on a PME system, and not being galvanically separated I have placed the required earth rod (my first ever in many years of sparking!) adjacent to the system connected using 10mm csa earth wire to strategic points on the support frame.
The question is' using my Megger 1553, how do I test this earthing arrangement and what readings are allowed for DC circuits?
Should I test it similar A.C. TT system ie: RCD is 30ma so 50v/30ma = max 1666 ohms
(or should I be aiming for under 100 ohms as recommended on other posts on this site), is it different (earth path wise) when reliant on a DC circuit to create the fault current?.
Confused!
Thanks in anticipation