Got my MCS inspection on the 24th March and I'm struggling with earthing the array frame.
I have installed an SMA 4000tl inverter on a PME system, and not being galvanically separated I have placed the required earth rod (my first ever in many years of sparking!) adjacent to the system connected using 10mm csa earth wire to strategic points on the support frame.

The question is' using my Megger 1553, how do I test this earthing arrangement and what readings are allowed for DC circuits?
Should I test it similar A.C. TT system ie: RCD is 30ma so 50v/30ma = max 1666 ohms
(or should I be aiming for under 100 ohms as recommended on other posts on this site), is it different (earth path wise) when reliant on a DC circuit to create the fault current?.
Confused!

Thanks in anticipation
 
Unless you have the earth rod testing options the only other way to test the stake is by doing your standard Zs test, using the stake as your earth connection.

As for what would be a good value, BS7671 states earth stakes should be less that 200 ohms (for stability) whilst the NICEIC say aim for 100 ohms. If I got less than 200 that'll do for me! Unless your unlucky with soil conditions etc. getting less than 200m should be straightforward.
 
You are right 1st solar. BS7671 states the maximum Zs for a 30ma rcd is 1667 ohms. Still, as pointed out by my NICEIC inspector one time, would you accept a reading above 200? if not then you have your answer.
 

Reply to Earth Rod Readings in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
805
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
899

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top