When testing a tt system, if you cant locate the earth rod is it ok to carry out a ze test for that supply and put a limitation in the earth rod section of the test cert.

if not can anyone suggest how to obtain the correct resistance measurement with only the earth cable at the board accesible.

thanks
 
If you are doing an EICR and the rod is under paving or floorboards, then you are a bit stuck, however this would be an operational limitation.
But it is a critical safety point so if you can find it it would help, if you are unable to check the labeling and security of the connection you do not know how safe it is.
But if you are getting a decent Ze reading then at that time it is OK.
Probably a further investigation required.
 
thanks richard.

do you think the ze measurement would be representative of the resistance reading for the rod, or is this an assumption that cannot be made.

I am happy to put a limitation in the section regarding the type of rod etc but a figure in the resistance of the rod would be good.

Would the ze be this figure.
 
Ze is an acceptable estimate for the true Ra of a rod, the difference in resistance will be likely less than 0.5 ohms (the resistance of the line conductor back to the substation) and will not make a significant difference to the value.
 

Reply to earth rod test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top