So you can use the armour OF SWA IN DIS CIRCUIT AS bonding conductor if it is sized correctly, is there a table for this or can i see where this is and work it out for myself.. Maybe with help from yourself with my buts and whats, y
 
I have my own table, cant remeber where i got it from but it shows you the cross sectional areas of swa required as an earthing conductor along with what size is suitable and what isnt.
 
So you can use the armour OF SWA IN DIS CIRCUIT AS bonding conductor if it is sized correctly, is there a table for this or can i see where this is and work it out for myself.. Maybe with help from yourself with my buts and whats, y

I'm getting confused here. If I was main bonding services in the extension I would be running a separate earth conductor from the MET............end of. Is it because the supply is to a DB and not a load that he is allowed to use the armour as a bonding conductor??
 
I'm relieved it was a DB. But like we both said, separate Earth for main bonding.............I wouldn't do it any differently regardless of what I've seen.
 
yeah i agree. but you cant legislate for the way other people do things sometimes, especially when they dont do it the way you would do it and your trying to find a fault. :)
 
So for my 16mm 5c swa as im not using swa as cpc i could use it as bonding conductor as it would be equivelent to 31mm copper

meaning i could run bonding to this board instead of back to met at service fuse?

Could i use armour as cpc and bonding conductor in this case
 

Reply to Earth Size etc? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
546
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

He needs to first be able to confirm the design current (Ib)
Replies
6
Views
840
No table I just know the conductivity of the armour is around 4.0mm² copper equivalent so 6.0mm² will be fine.
Replies
6
Views
411

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top