No probs. I dont see why not, ive never seen it stated anywhere that an armour cant be used as a main bonding conductor providing the connections are sound and id probably label it so when its periodic is due its not flagged up. As ive said in a previous post its not the way id do it but i have seen it done that way before.
 
Depends where your main earth terminal is, if its within say an mccb panel id use whatever size link the bonding conductor was that was required, plus you'd have the metallic frame of the db.
 
Hi Guys
Thanks for all your interest. First, cost is a factor on this job (isn't it always!) Client thought he could just have a 1ph supply and a domestic CU. lol. Requirements have changed today (again)!
Yep, you're right! You've clarified my muddled thinking! Best is a 3ph board, 4 core SWA using the armour as earth. I can just about balance demand across all phases. Max 35 amps/ph so may even drop to 6sqmm ( with 40 Amp fuses in the switchfuse) after checking volt drop calc. Whether 10sqmm or 6sqmm I think I'm correct in saying that the Cu equivalent csa of the armour on both sizes is 13.5 sqmm and 11.5 sqmm respectively so no seperate earth required.
Re bonding - none required at the mo. - no extraneous services/steel (water only in plastic).
I assume that if bonding is required, I have to take a seperate 10sqmm conductor all the way back to main earth terminal in the meter cupboard?

Cheers
Pete

As this is a PME installation, it's the bonding side of things that complicate things when extraneous services etc are involved!! As there aren't any in this case, continue as if this is a TN-S supply!! The armour of the SWA cable is more than suitable for the CPC and probably the earthing arrangement at the DB, but as always this should be confirmed by calculation/measurement etc!!


One thing to point out on this thread, Bonding requirements need to be related back to copper equivalents when talking about using any other type of metal conductor. They can't be mixed either, so you can't use the SWA and a smaller copper conductor to comply with minimum mm CSA.... Either the copper conductor needs to be of sufficient CSA to carry the full fault current, or the armouring needs to be of a sufficient CSA copper equivalent...
 
Last edited by a moderator:
As this is a PME installation, it's the bonding side of things that complicate things when extraneous services etc are involved!! As there aren't any in this case, continue as if this is a TN-S supply!! The armour of the SWA cable is more than suitable for the CPC and probably the earthing arrangement at the DB, but as always this should be confirmed by calculation/measurement etc!!


One thing to point out on this thread, Bonding requirements need to be related back to copper equivalents when talking about using any other type of metal conductor. They can't be mixed either, so you can't use the SWA and a smaller copper conductor to comply with minimum mm CSA.... Either the copper conductor needs to be of sufficient CSA to carry the full fault current, or the armouring needs to be of a sufficient CSA copper equivalent...

Whereabouts does it state that? just for my future reference, never been able to put my finger on it. Cheers
 
Resistivity factors should be telling you this, without needing it to be laid out in black and white!! Steel has a far higher resistance value than that of copper, so mixing CSA's of the two metals is a complete NO, NO!! That's not to say that you don't earth the SWA, just don't use it as a make-up for bonding purposes, it'll be acting purely as a CPC!!
 

Reply to Earth Size etc? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
544
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
758
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

He needs to first be able to confirm the design current (Ib)
Replies
6
Views
840
No table I just know the conductivity of the armour is around 4.0mm² copper equivalent so 6.0mm² will be fine.
Replies
6
Views
411

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top