Can someone please tell me what the current standard os for earth bonding. On several installations, electricians have run a separate earth wire to a machine or isolator, rather than relying upon the wire armour of the cable. I have a client who has a diesel metal storage tank, complete with electrical pump. There is no earthe bonding to the tank, only the wire armour of the cable.
 
Yes in some instances, the armour of an SWA cable can be sufficient to be used as a bonding conductor.
With TT and TN-S, the minimum CSA of armour required is 48mm² and with TN-C-S 80mm².
 
Just looked on another thread about diesel tanks their tank was plastic presume they had some sort of metal pipe fitted some where, but if the tank is on concrete block wall as some of them are or plastic if u can prove its not earthy do you need to bond it?
 
Earthing and Bonding are two distinctly different issues, you seem to be straying in to both,are you asking if the CSA of the earth in SWA is sufficient, or if the pipes and/or tank are a extraneous or exposed conductive parts ?
J
 

Reply to Earthe bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
I thought it was just a head with a link, rather than a fuse. Just strange that it can be so easy to pull it out. Different if it was a lid which...
Replies
3
Views
690
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top