YTSOxford
Installing 2 new 17th ed boards this week & Wanting to get your advice on earthing.
I usually connect the main equipotential conductors to the earth terminal in the board and then, if TT like this, from the earthing terminal to the rod. But this place has 24 circuits so i need 2 boards.
The earthing terminals in each board have one for the rod, and 2 for bonding. Would it be ok to put one of the bonding conductors in each board and use the second bonding terminal to interlink the 2 with 16mm G&Y, and have the Rod connected to the first CUs earthing terminal.
Bit of a headache to understand I know..in a nut shell, can i get around not having those ugly Earthing blocks with lots of G&Y???
Thanks all!