Earthing Arrangements Explained + Photo's

P

Paul.M

This is for the people still in or has just left their electrical education or for those of us that need a refresher in domestic earthing arrangements. It's all very well looking at prity diagrams in college and in books but its different when your out in the field for the first time. Hope this thread helps you and I hope that other members will post up their pictures of main incomers/earthing so others can learn and understand this subject better. I wish I could refer to something like this when I was in college.



First of all we have 3 types of earthing arrangements, TN-S, TN-C-S and TT.

TN-C-S
tncs1.jpg


This is where the main earth cable from the main earth terminal (met) is connected to the neutral at the suppliers main fuse. A good way to remember the name of this arrangement is to think of the C meaning COMBINED.


TN-S
image-3.jpg


This is where the main earth cable from the met is clamped or solderd to the steel of the SWA or the led outer sheath of the incoming supply cable. Again a good way to remember this is to think that the S stands for SHEATH.

TT
electrics_earthing_supply_types_and_bonding_meter_pos_tt-1.gif


The main earth cable from the met is connect to an earth electrode (aka earth rod). This is because not all properties are supplied with a TN system by the supplier so we have to insert a rod into the ground.


Notice how the earth cable on the TN systems go back to the main incomer, one goes to the main fuse (TN-C-S) and the other goes to the incoming cable (TN-S). If the main earth cable doesn't go back to the fuse or incoming cable it will be a TT. This is the simplest way I can put it without going into extended detail.



Now that we've seen some prity diagrams (am I starting to sound like a teacher lol) we will now look at real world photos that are not as straight forward as the diagrams.


First example, is it a TN-S or a TN-C-S or both?

IMAG0082-2.jpg
 
Last edited by a moderator:
It kind of looks like TN-C-S, plus an extra earth to the incoming cable sheath, as if the supply was once TN-S, but perhaps has been converted to TN-C-S?

Ten out of ten for SJD!

Yes its in an area where the DNO is installing TN-C-S to all the houses so at the time of the picture it was both so they could switch over without disconnecting an earth path from anyone's house. Just a good example to get the ball rolling on this thread.
 
If you have a neutral connected to an installations earth terminal (eg PME/TNC-S) then the incoming supply cables metallic sheath connection must be disconnected. Especially important where a supply cable is suppling both TN-S and TNC-S earthing arrangements!! eg, ....where the DNO cable is in the process of being PME'd....
 
TN-C-S

TN-C-S-system-photo.jpg


Another obvious one, were is the earth cable going? Ho to the main fuse therefore its a TN-C-S. C = Combined.
 
Last edited by a moderator:
its got to be an old tns changed to a pme but if think there its been left like that cause of corrosion to there incoming cable
i remember something the DNO mentioned to me a few months back regarding an installation query i had
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Paul.M,
Last reply from
LastManOnline,
Replies
177
Views
149,709

Advert

Back
Top