Alright, so what do you think of these CPC sizes in relation to the phase conductors?
90*C insulation, TN-C-S supply
MCB / Live / CPC / Multiplier
15 - 2.08mm2 - 2.08mm2 - X 1
20 - 3.31mm2 - 3.31mm2 - X 1
60 - 13.30mm2 - 5.261mm2 - X 0.3955
100 - 26.67mm2 - 8.367mm2 - X 0.3137
200 - 85.01mm2 - 13.30mm2 - X 0.1564
300 - 177mm2 - 21.15mm2 - X 0.1195
400 - 304mm2 - 26.67mm2 - X 0.0877
500 - 456mm2 - 33.62mm2 - X 0.0737
600 - 760mm2 - 42.41mm2 - X 0.0558
0.3, 0.1 and 0.05 multiplier difference ever encountered in the UK?
Can you explain what 5E5 and the number in the I2R column mean?
US breakers do not always trip magnetically either due to the run length or high pickup. Some older breakers did not have a magnetic trip.
You make a valid point about high current, I was thinking about low current from long runs but ultimately I need to consider both.
The smaller sizes (60A and below) look OK for C-curve MCBs which would be expected anyway. But those would be limited in the UK to typically 6kA domestic or 10kA commercial max PFC.
It would be unusual to be taking smaller cables direct from a crazy-high PFC board anyway, usually a board with ~1kA load and tens of kA PFC would feed ~100A sub-boards for low current end circuits, and by then the PFC is somewhat more sane to wrangle with a MCB.
It would be unusual to be taking smaller cables direct from a crazy-high PFC board anyway, usually a board with ~1kA load and tens of kA PFC would feed sub-boards for low current end circuits, and by then the PFC is somewhat more sane to wrangle with a MCB.
Agree.
FWIW in some cases you do have 3.31 and 5.261mm2 wire coming out of a 22ka or 65ka panel board though fortunately its not ultra common.
Wow, that looks scary to me!
I know some MCCB also have HRC fuses to act as ultimate peak fault current limiters, but I suspect those in your picture are just normal therma-magnetic MCCB.
It is just the I2t values scientific notation, sometime in lazy format. So:
500,000 = 5 * 10^5 = 5.0E+05 = 5E5
No magnetic trip sounds like an utter disaster for any usable protection. The thermal element is simply not fast enough (unlike a fuse, but its heating element is on a one-way trip to vapour).
Yes, your worst-case is not always the highest fault.
Usually fuses decrease in I2t as you go from low overload / long disconnect to high current fast faults. There it is the longest time (highest Zs, etc) that is worst.
MCCB & MCB have two regions, the thermal one is quite slow so the 't' in I2t is large, and while the magnetic trip is fast at ~10ms in many cases, it does not get faster or limit the fault current to a great degree as PFC goes up. So typically your worst-case points in the breaker design is either max PFC, or just below the magnetic trip point where 't' is long but 'I' is fairly high.
I'm still confused as to what the I2t limit represents. Joules?
I will go trip curve hunting- however- I think my eyes were just opened again... you might be right. As in spot on. But I'm still willing to challenge the concept. ?
Ok- here is a commercial/industrial US breaker trip curve:
If I'm reading the above time current curves correctly:
0.8 disconnection time on thermal takes about (roughly) 15x the handle rating worse care.
0.4 disconnection time on thermal takes about (roughly) 22x the handle rating worse case.
Assuming a 20 amp breaker-
15 x 20= 300 amps. At 120 volts a loop of 0.4 ohms is required.
22 x 20= 440 amps. At 277 volts a loop of 0.62 ohms is required.
A 500 foot circuit run consisting of 3.31mm2 wire has a R1+R2 of 2 ohms.
3.31mm2 wire has an 60Hz AC Resistance of 0.002 ohms per foot at 75*C.
At 120 volts I am limited to a 100 foot run. (30 meters)
At 277 volts I am limited 50 a 155 foot run. (47 meters)
Not unrealistic for a good chunk of circuits.
Technically I am incorrect to use 120 and 277 volts in that supplies vary below this value, but at the same time a 75*C resistance covers it reasonably well for the discussion at hand IMO.
Am I correct to conclude that it is indeed possible to provide adequate disconnection times with US breakers when the fault current does not trip the breaker magnetically? Or is this just me being overly wishful?
My mind keeps telling me that it is possible to achieve 0.8 and 0.4 with thermal elements. But I am humble in my argument. ?
The units are 'Ampere^2 second' and it represents Joules per ohm of resistance.
So if you know the resistance per unit length of your conductor (from material resistivity and cross sectional area) it allows you to compute the resulting fault energy per unit length. Then from the specific heat capacity of the material and its mass per unit length you can compute the change in temperature that fault energy causes.
From knowledge of the starting temperature and the peak short-term survival temperature of the cable (typically decided by the insulation type) you can decide if that fault is going to permanently damage the cable or not (i.e. will the fault delta-temperature exceed your operating margin).
In most cases the material properties (resistivity, specific heat capacity, temperature limits) are combined in to a single constant 'k' that is used in the adiabatic cable equation.
Yes, it looks like that.
It has a magnetic trip as well, but not coming in until very high. It also appears (from my reading of the plot) that the magnetic trip is fixed at about 540-900A (36-60 * 15A) as you see the 30A range is about half of the multiplier.
That sort of fixed-magnetic approach is not uncommon for MCCB over here, but our MCB all have the magnetic trip at a set ratio of the thermal trip (our B/C/D curves). That example USA breaker is above our D-curve (10-20 * In) by a factor of almost 4 at 15A and 2 at 20A.
In UK domestic installations is is rare even to see C-curve being used, and D-curve is usually restricted to very high inrush things like big transformers or motors.
Those look right and reasonable, though you have not allowed for the supply impedance (probably quite small for USA with 200A boards and TN-C-S style of connection as common).
Yes, voltage range and starting temperature for working resistance would reduce that distance by 20-30% or so.
You are right that they can meet our sort of disconnection times on the thermal part. But are doing so at far higher currents than we would expect to see without the magnetic part tripping.
Much of your example thermal curve is "inverse time" and approximately constant I2t, so a reasonably good match for cable protection. But it is allowing of the order of 45k A2s let-through for a 15A breaker, and we would only expect to see that sort of a fault energy at PFC of around 10kA, or at around 40A when it is quite slow to trip and some of the fault heat is able to escape (so less "adiabatic" in the true sense).
Your observation is correct, the magnetic trip pickup values are fixed for a lot of thermal magnetic breakers across the product line meaning 15-30, 40-70, 80-125, ect all have the same magnetic pickup with only the thermal portion of the breaker differing to match the handle rating. Not all breakers, but roughly about 40-50% of the market.
Here is another example of a fixed magnetic pickup:
https://download.schneider-electric...ng&p_File_Name=50-01.pdf&p_Doc_Ref=0050TC0401
From what I've been told the (but can't confirm) is that the magnetic pickup is primarily intended to protect the panel board's busbars and supports from short circuit stress during high current faults.
If I am correct France is big on type C breakers for socket circuits.
I did leave out Ze in those equations which would change the values by 5% having run the numbers. Typically the transformer is close to the building with over sized service conductors so Ze tends to be negligible in comparison.
Its good/comforting to know that US breakers can meet disconnection times on thermal pick-up alone. However as I've said before the NEC does not restrict circuit length so it is legally possible to exceed 0.4 or 0.8 seconds.
My biggest concern however which had me start this thread are the size of the CPCs mandated under the NEC. While I am fairly confident that high short circuit levels will prevent the CPC from over heating longer circuit runs and slow thermal trip could push the CPC over 150*C (the recommended temperature limit) during a short circuit.
For example, 2000 amps on a 13.3mm2 CPC (200 amp breaker) for 5 seconds would heat the conductor substantially.
Any idea of the k factor for my wires above?
A quick search pulls this up with a lot of details:
For copper wire and 70C PVC (common case) then k=115
OK, that makes sense from a production cost point of view. Probably similar argument for MCCB, but there the use of a very high magnetic trip point can help with selectivity (depending on down-stream fault impedances)
Possibly. But commonly they use 16A/20A for a few radials, where as we tend to have 32A B-curve on a lot of sockets with individual HRC fuses in the 3-13A range.
To me that the the main issue - that proper design to meet shock and overload safety is not always applied. Then fancy electronics is added to try and fix the results of that...
Yes, the CPC table you started with looks awfully small for the larger breaker sizes (100A and above).
They are usable, but only just when the disconnection let-through is carefully controlled. To me that is not good enough for "rule of thumb" as that ought to be safe for all common combinations, and going to smaller CPC ought to be part of detailed analysis to justify it.
Earth
Earthing Conductor Size- Good?
Cookie,
Cookie,
TrueNAS JBOD Storage Server