Earthing flexible water pipe

Hi All, I'm not an electrician (this will soon become apparent), but I am a homeowner with an electrical query. Several years back I had a bathroom renovation done, which amongst other things, resulted in some copper pipe suppling my basin to be replaced with flexible hose. The earthing/bonding clamps that were originally connected to the copper were left unattached as there is essentially no copper pipe exposed to which they can be attached. I've attached a photo. Is there anything that needs to be done to correct this?
Thanks in Advance.

20240908_152454 - Copy.jpg
 
If all the electrics in the bathroom are protected by RCD's or RCBO's, then you no longer need supplementary bonding.


Why are the flexible tails scorched by heat? Its not like theres any soldered joints there?
 
If all the electrics in the bathroom are protected by RCD's or RCBO's, then you no longer need supplementary bonding.


Why are the flexible tails scorched by heat? Its not like theres any soldered joints there?
OK, thanks for the input.

I don't think that's heat damage, although I've not lived in this property for some time. It feels like rust/corrosion on the braiding. Could well do with being replaced.
 
you might be right about rust....


can you confirm if the bathroom electrics are rcd protected?

Supplementary bonding was the norm several years (decades) ago... when every piece of metal was linked together with 4mm earth wire... from the light fitting, radiators, shower, hot and cold at bath, hot and cold at basin and even the bath itself if it was cast iron.... Some even took it to aluminium window frames....

Nowadays, with the increase in use of plastic water pipes and fittings, along with the RCD's... its no longer a requirement
 
you might be right about rust....


can you confirm if the bathroom electrics are rcd protected?

Supplementary bonding was the norm several years (decades) ago... when every piece of metal was linked together with 4mm earth wire... from the light fitting, radiators, shower, hot and cold at bath, hot and cold at basin and even the bath itself if it was cast iron.... Some even took it to aluminium window frames....

Nowadays, with the increase in use of plastic water pipes and fittings, along with the RCD's... its no longer a requirement
There's a fixed RCD on the consumer unit with test button. I'm assuming it covers all the circuits (this is a small flat) but I need to do a bit of homework on how all that works. I appreciate the input though.
 
There's a fixed RCD on the consumer unit with test button. I'm assuming it covers all the circuits
If there's no main switch on the CU, then the RCD is doubling up as the main switch and everything is protected by it. If there is a main switch and MCBs between it and the RCD, then one or more circuits served by the MCBs at the main switch end of the row probably aren't protected.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Nimonic,
Last reply from
brianmoooore,
Replies
5
Views
1,072

Advert

Back
Top