Hi all,

I'm in need of a bit of clarity on this decision.

So, long story short... have been asked to quote for the installation of some electrical services. Property is a small holding, my bad, but didn't check existing earth as there was a lot of items discussed (given it's location, I suspect it's TT as it's an overhead supply), but key ones are provision of various bits outside in a barn and a shed. Barn is attached to property, shed is not. So, I'm planning a small plastic CU inside a weatherproof steel cab inside the barn, fixed wiring will be SWA to try and reduce rodent problems.

My plan is to provide an earth in the vacinity of the barn by way of a rod or structural steel that penetrates the ground (if there is any, not sure there is). If the structural steel doesn't penetrate the ground, I'll be bonding it anyway. Thus creating a TT installation for the outdoor power.

Supply to barn is from main CU by way of a 30mA RCD protected circuit, so I don't need to worry about localised RCDs. I know it would be preferable to have the RCDs local to the board, but the cable is already in place, it's T+E and runs through the building so I'm inclined to leave the RCD at the source.

Am I on the money or way off? If you guys need more info, please let me know and I'll be happy to provide :)

Thanks
 
Hi,just a quick glance,and i am afraid the SWA is not rodent proof,if they are an issue,they will open the armouring to corrosion everywhere they nibble. Maybe consider some containment of a galvanised variety? :)
 
Hi,just a quick glance,and i am afraid the SWA is not rodent proof,if they are an issue,they will open the armouring to corrosion everywhere they nibble. Maybe consider some containment of a galvanised variety? :)

I have considered conduit, I think the price may put them off. To be honest, she mentioned a rodent problem (and there was some evidence a cable being damaged near ground level), but around the barn, the cables already there (not connected) are T+E and I saw no other evidence of meeces, so I'm fairly happy with the choice of SWA. I wouldn't be using the armour for earthing (I prefer not to) just for the additional mechanical protection.
 
You may find that even with overhead supply there's a pme. A lot round here have.

Yeah, I'm seeing overheads converted to PME here too, but 705.411.4 states TN-C system shall not be used (705 is relevant because there are animals present), so unless I'm misunderstanding this regulation I'm required to use TT earthing for this work.
 
What will the barn be used for? Any possible livestock involved?

There is a yard with chickens, two pygmy goats, some guinea fowl, a couple of donkeys in the field next door, so I think yes :)

It was the old milking barn, still got some of the old machinery in there.

This is why I was referring to section 705.
 
Hi
I wasn't considering the full implications of your design. Just a general observation on overheads and pme. I'm sure there's no misunderstanding on your part.
Have fun.

That's why I'm asking though... I'm not sure whether my interpretation (and thus my proposed solution) is correct.

In the space of a week, I've got two jobs come up, one on a working farm and the other on this small holding, where I've got the issue of earthing to seriously consider so I'm just wanting to double check my thinking.
 
Yeah, I'm seeing overheads converted to PME here too, but 705.411.4 states TN-C system shall not be used (705 is relevant because there are animals present), so unless I'm misunderstanding this regulation I'm required to use TT earthing for this work.
You can use TT, TN-S or TN-C-S but certain requirements are needed should the latter be employed and some suppliers may not provide TN-C-S for agricultural sites. TN-C is the only system not to be used and I have yet to come across this in the UK.
 
You can use TT, TN-S or TN-C-S but certain requirements are needed should the latter be employed and some suppliers may not provide TN-C-S for agricultural sites. TN-C is the only system not to be used and I have yet to come across this in the UK.

Then I was misunderstanding that as I was assuming it was a short form for TN-C-S... and I must admit I did ponder what other TN-C-? it could have been other than TN-C-S, so I've learned something today :)

But on a serious note, have been doing a bit more reading about this I don't have a suitably sized earthing conductor that I can connect to the MET at the incoming supply, regardless of earthing system in use, and getting one from one corner of the house to the other will be a problem.

So, I'm going to install a rod (or use the metal structure of the barn if it is in good contact with the earth) and create a TT earthing system for the external electricals, which will include bonding the metal work of the barn.
 
The "certain requirement" for using a TNC-S could be rather expensive.

This is taken from :

Electrical Contractors guide to wiring Regs 17th edition. (Does not include amendments)

If a bonded metal grid cannot be laid in the floor of animal houses during construction or refurbishment, it is recommended that a TN-C-S (PME) electricity supply is not used. A TN-S supply is preferred. If a TN-C-S supply is offered or is the only type available, it is recommended that a separate local earth electrode be installed.

I think your ok with your design but don't take my word for it.
 
I like the TT solution for remote agricultural buildings. The barn is attached to the dwelling and so it should have a metal containment for the CU as you say. But there's a 5 way IP rated metal one from BG that's good value, if it was big enough.
Bg - Search Results | Screwfix.com - https://www.screwfix.com/search?search=BG

[ElectriciansForums.net] Earthing for an outdoor install in a barn
 
Last edited:

Reply to Earthing for an outdoor install in a barn in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

We do have consultancy, but not for such like. The question could be put to the UK property manager, I’m just wondering what you guys have been...
Replies
2
Views
433
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top