What about supplementary bonding what size cable and do you have to do it in a TT ?

Think you've gone a little off topic on this one mate! If he doesn't do TT he would than have to contact the DNO to provide an earth (if they can) and than he could be waiting weeks, even months. Besides if he sets up a decent TT system what's the need to change!!
 
There is a lot of different point being raised here not sure if it is answering the question posed. We appear to be discussing the main earthing conductor, the protective bonding conductor, supplementary conductors and any other earthing conductor

The main bits from the regs

542.3 Earthing conductors
542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor. In addition, where buried in the ground the earhting conductor shall have a cross-sectional area not less than that stated in Table 54.1. For a tape or strip conductor, the thickness shall be such as to withstand mechanical damage and corrosion

Table 54.1 – Minimum CSA of a buried earthing conductor say
Protected against corrosion by a sheath & mechanical protection – 2.5mm² if copper
Protected against corrosion by a sheath BUT no mechanical protection – 16mm² if copper
NOT protected against corrosion by a sheath BUT mechanical protection – 25mm² if copper
NOT protected against corrosion by a sheath & no mechanical protection – 25mm² if copper

543 Protective conductors
543.1 Cross-sectional areas
543.1.1 The cross sectional area of every protective conductor, other than a protective bonding conductor, shall be:
i) Calculated in accordance with Regulation 543.1.3 [S=√I²t/k]
or
ii) Selected in accordance with Regulation 543.1.4

543.1.4 Where it is desired not to calculate the minimum cross-sectional area of a protective conductor in accordance with Regulation 543.1.3, the cross-sectional area may be determined in accordance with Table 54.7

Table 54.7 say
CSA of line conductor 16mm² protective conductor same size

CSA of line conductor 16mm² 35mm² protective conductor 16mm²
CSA of line conductor 35mm² protective conductor half the size of line conductor

Protective Bonding Conductors
544.1.1 Except where PME conditions apply, a main protective bonding conductor shall have a cross-sectional area not less than half the cross-sectional area required for earthing conductor of the installation and not less than 6mm². The cross-sectional area need not exceed 25mm² if the bonding conductor is of copper or a cross-sectional area affording equivalent conductance in other materials

544.2 Supplementary bonding conductors
544.2.3 A supplementary bonding conductor connecting two extraneous-conductive-parts shall have a cross-sectional area not less that 2.5mm if sheathed or otherwise provided with mechanical protection or 4mm if mechanical protection is not provided, except that where one of the extraneous-conductive-parts is connected to an exposed-conductive-part in compliance with Regulation 544.2.2, that regulation shall apply to the conductor connecting the two extraneous-conductive-parts
 

Reply to earthing for tt system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
799
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
658

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top