Is it a requirement of BS 7671 to Earth SWA cable at both ends when using an integral conductor as a cpc. I don't think it is and can't find a reg which states that it is but wondering if someone could help clarify.

I was once told it was good practice to earth at both ends when using an integral cpc in case the armouring and cpc had a difference in potential and both were touched simultaneously during an earth fault prior to the disconnection device operating.

Any thoughts?
 
It is definitely good practice yes.
If the SWA is the CPC then obviously a good connection at both ends is essential. If the SWA is not the CPC it is still an exposed conductive part and must be earthed. This can be achieved by earthing at one end, usually the supply end. I always earth at both ends regardless.
 
If earthing at one end it should be the supply end of the cable as far as I know.
Earthing at both ends is not necessary, but it will help lower Zs.
 
It is definitely good practice yes.
If the SWA is the CPC then obviously a good connection at both ends is essential. If the SWA is not the CPC it is still an exposed conductive part and must be earthed. This can be achieved by earthing at one end, usually the supply end. I always earth at both ends regardless.

Is it?
 
The steel is covered by an over sheath of insulation so is not exposed. The SWA glands are an exposed conductive part until covered by the shroud.

This was always a point of mine whilst learning. My mentoring electricians and lecturers always maintained that the shroud was not sufficient to be relied upon to guarantee the gland would never be exposed, and that the gland, and by extension the armouring, were to be considered exposed conductive parts.

Possibly just a twisting of regulations and definitions to ensure best practice, but it's the way I was shown.
 
This was always a point of mine whilst learning. My mentoring electricians and lecturers always maintained that the shroud was not sufficient to be relied upon to guarantee the gland would never be exposed, and that the gland, and by extension the armouring, were to be considered exposed conductive parts.

Possibly just a twisting of regulations and definitions to ensure best practice, but it's the way I was shown.

A cable tie top and bottom of the shroud (doesn't look professional though) lol.


EDITED -Leesparkykent - you know the rules in the main forum for swearing, no matter how you spell it to try get around the software detection it is still not allowed, Ive altered it for you :).

Darkwood.
 
Last edited by a moderator:
[COLOR=#ff0000 said:
EDITED[/COLOR] -Leesparkykent - you know the rules in the main forum for swearing, no matter how you spell it to try get around the software detection it is still not allowed, Ive altered it for you :).

Darkwood.

Oops! :ban:Lol
 

Reply to Earthing SWA at both ends in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
597
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
377

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top