Hi all

Just wondering why a lot of people on here say you should only earth swa at one end. If this happens what happens to the other end which isn't earthed? Is the armoring connected to gland then left doing nothing with 3rd core of cable providing earth. I thought the idea to the armouring was for it to be earthed :confused: sorry if its a daft question! reason i ask aswell is that i have an swa termination to do soon on a tncs supply so want to get right

cheers
 
Hi all

Just wondering why a lot of people on here say you should only earth swa at one end. If this happens what happens to the other end which isn't earthed? Is the armoring connected to gland then left doing nothing with 3rd core of cable providing earth. I thought the idea to the armouring was for it to be earthed :confused: sorry if its a daft question! reason i ask aswell is that i have an swa termination to do soon on a tncs supply so want to get right

cheers

Hi. I've not read the post about terminating one end. It might be that they are going to put an earth rod in. And then it is recommended to disconnect the earth to the house so as to avoid the fault being diverted along the armoured back into the house. And forcing it down to earth via the rod.
 
Hi. I've not read the post about terminating one end. It might be that they are going to put an earth rod in. And then it is recommended to disconnect the earth to the house so as to avoid the fault being diverted along the armoured back into the house. And forcing it down to earth via the rod.

whats your methods when running swa from consumer unit to metal consumer unit in garage, earth both ends?
 

Reply to Earthing Swa one end in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
715