Where do you stand with adding circuits to a installation that has the bonding undersized? It's in 6mm and should be 10mm to be up to regs but customer doesn't want it replaced? Can I do the work and advise this should be replaced it's tnc-s
Where do you stand with adding circuits to a installation that has the bonding undersized? It's in 6mm and should be 10mm to be up to regs but customer doesn't want it replaced? Can I do the work and advise this should be replaced it's tnc-s
Regulation 999.1: "Where good quality carpeting/flooring is in use, undersized main protective bonding conductors may be utilised where the installation of correctly sized main protective bonding conductors may result in damage to these furnishings"
Regulation 999.1: "Where good quality carpeting/flooring is in use, undersized main protective bonding conductors may be utilised where the installation of correctly sized main protective bonding conductors may result in damage to these furnishings"
And if the above is not observed please note regulation 999.2:- Ensure that you have adequate home insurance to replace your nice furnishings in the event of an electrical fire due to inadequate earthing system.
IQ you should write your own regs, there better than the ones we have now
Regulation 999.1: "Where good quality carpeting/flooring is in use, undersized main protective bonding conductors may be utilised where the installation of correctly sized main protective bonding conductors may result in damage to these furnishings"
Your options are as in post 2, if you choose to do the work, make sure you have documented the undersized bonding on your certification and maybe also a covering letter to the client advising of the need to upgrade.
The requirement of BS7671 is to ensure the earthing and bonding arrangements are adequate for the safety measure used.
Adequate does not necessarily mean compliance with BS7671.
the adiabatic isnt used to size main bonding conductors, use it to size the main earth then the tails and bonds can be sized in relation to this and the size of main service fuse and if adequate then they can be left at 6mm and noted on the eic.