pme is a bit awkward
the adiabatic isnt used to size main bonding conductors, use it to size the main earth then the tails and bonds can be sized in relation to this and the size of main service fuse and if adequate then they can be left at 6mm and noted on the eic.
Got a similar scenario myself went to have a look at a fuseboard change earthing to water is in 6mm looked at the ways of upgrading it to 10mm not a chance tiled floor above kitchen and position of sink opposite to the outside of the house do i just note it down on the eic
i would test all the earthing arrangements and if they are ok and test out,give the 6mm earths a code 4 on your cert.
sorry i meant to say add a remark about the bonding on your cert and word it as a code 4 .