E54,I'm interested to know what value of Ra you would accept.given that a 30ma RCD will provide earth fault and additional protection up to 1667 ohms..(in theory!)...why is an Ra of 200 ohms not acceptable?
Unless you achieve an Ra of <5 ohms ,for example,the typical OCPD,s on final circuits will not reliably operate in an acceptable time under earth fault conditions. Therefore you are likely to be reliant on the RCD.
It seems to me that the RCD will operate in exactly the same way whether the Ra is 5 ohms,or 200 ohms.....so why bother with 5 ohms?

The question I am asking is what is your maximum Ra....and why that value?...discuss....:smilewinkgrin:

Sorry for the delay in replying wirepuller, i fell asleep as i'm also up-dating my monthly project report, i just keep the forum running in the background, and come back from time to time when i need a break. ..lol!!!

Let me start of by saying that i don't particularly like to see a TT system on domestic installations full stop, especially in the UK!! The art of creating a good TT system there, seems to have been lost since it was common practice in the rural and suburb areas of towns. Then it was common practice to aim for a 10 to 25 ohm Ra and depending on the sparks, ...often achieved better. These day's it's just not economically viable in many cases on a domestic installation, But that's not to say that a decent attempt should not be made, by at least using a DEEP driven rod, of a suitable depth and not just bunging in a super thin 1.2m rod in the ground, that in all honesty is a total waste of time!! ...

What i personally try and achieve on a TT system is a low enough Ra to trip a socket circuit on say a 16A/20A MCB, in several seconds and lower rated MCB's in 5 sec, (although an MCB can trip anywhere on the instantaneous portion of it's T/C characteristic) which was a little easier on the older type 1 MCB's and BS 1361 fuses, than it is with the new type B MCB's.

I'm not trying to meet the new or old TT system disconnection times, based on RCD protection. I would however be trying to give the installation a degree of protection should a RCD fail for whatever reason, ie ''Addition Protection''. We must also remember that disconnection times rely on the installations Zs and not necessarily on the Ra/Ze alone when a RCD fails.

I've never said that installing a good/decent TT system is going to be cheap, it's not, certainly not in the time taken to install one. Depending on the soil resistivity and conditions, could further add to costs, in terms of materials... However, i'm fairly confident that given say 4 X 3m 3/4'' rods i could achieve an Ra value of 3 to 5 ohms in many parts of the UK, and in some area's that i know, below 1 ohm, with less rods. Depending on the soil conditions, that may well also require electrode enhancers and/or modern soil conditioning chemicals.

So what does a 200 ohm Ra give you?? Absolutely nothing really, ...It achieves a 50V touch/threshold voltage, only while a 30mA RCD is functional!! The lower the Ra, the better the chance of limiting the touch/threshhold voltage that will be present in a fault condition... I can't say i know of any other national code or Reg, that has such a high max Ra value of 200 ohms. The States and Canada require 20 ohms, even France wants to see a max of 100 ohms, and they use 500mA RCDs on domestic installations....

As it so happens, we are in the final throws of completing a number of ground fields on my project, with a contract specification level of max 1 ohm for each of the ground fields, which was achieved on all of them, before all of the rods being placed. The highest ground field to date, coming in at 0.38 ohms and when all are connected together by a site ring (before connecting all project buildings) of 240mm, i've roughly calculated a final Ra of around 0.17ohms. OK, so i'm far happier working with extensive TT systems, than the much smaller ones, but even they can be made/designed to provide a decent and stable measure of protection. As mentioned earlier, it just depends on how much time and of course money you, and the customer wants to invest in the installation. I know what i've managed to achieve with relatively little monetary cost, but with a fair bit of time at my house in Cyprus and with pretty bad soil conditions too, (soil resistivity of 650+ ohm/m). (in
I know full well that you disagree on the value a good TT system can bring to an installation, based on the time and cost, and that you would prefer to trust that RCD totally, to provide your earth fault current protection, whereas i wouldn't. Which is why it is better to agree to disagree, because i'm sure we are not going to change our thinking on the matter...lol!!!
 
Thankyou for your very informative reply E54....I would entirely agree with you that if an Ra of substantially less than 10 ohms,or even TN values of Ze can be achieved then the OCPD operating in case of RCD failure within a reasonable time would be an advantage.....I think though,as you imply,on the typical small TT install usually queried on this forum such values are not practical or cost effective.
My argument is with "higher" low values which some people insist should be aimed for,such as the 25 ohm vaue you gave as an example. Such a value would give you an PEFC of 9.5A on a 230v supply....that wont trip a 32a mcb and would take around 400s to trip a 6A/B......not much use really. Therefore you are still dependant on the RCD,so what is the advantage over an Ra of 200 ohms?...personally I cant see one.
To sum up I totally agree that low enough Ra's to operate an OCPD quickly are an advantage....but Ra's still considered low, but way to high to operate an OCPD are a waste of time and money trying to achieve as they offer no advantage over Ra's of 100-200 ohms.
 
I can see where your coming from, i can honestly, but don't just think in terms of ultimate Ra values. A good Ra value will almost certainly help in Zs values in the smaller TT systems so a stable 20/25 ohm Ra can and will help disconnection times that are based on Zs values. It will also go a long way in clamping or limiting the touch/threshold voltage. Every installation is going to be different, it just needs a level of competency to access and provide each installation with at least a working earthing system and not a dormant one.

I can't see why, the installation of a decent length of earth electrode can't be a dam site more beneficial than installing a earth rod that is too short and too thin to give an installation any overall benifit or any longevity. For sure, they will never in a month of Sunday's provide a stable Ra value, it's will be up and down more times than a ------ draws during the course of a year!! lol!! For me, they should either be removed from the market place, or an Ra level set, that would make them impossible to comply to the requirements.
 
Just a small point
XLPE SWAs are used now in the UK more and more, Any (most) sizes larger than 6mm2 will not comply with fault protection which means that the maximum size realistically would be 6mm2 and then you would have to run a separate protective bonding conductor .

I just re-read your post reply, maybe this was an addition written after your initial post?? But this statement is totally Wrong! I'm not sure where your information is coming from, but the armouring of either 70C PVC or 90C XLPE 2 core SWA cables DO COMPLY for use as the CPC. 3 core 10mm SWA cables and above will comply with both equipotential bonding and CPC provision for the cable (Please check the sticky section on this subject (above) particually the tables in the link within post #37 by spinlondon)

I notice that you and some others, often use the term ''CPC'' when referring to equipotential bonding conductors. They are substantially different animals in fact, and perform totally different roles within an electrical installation and should never be confused with each other.
 
on a tt installation can you run a 2 core cable to the shed and drive another spike in the ground outside the shed? If you do this is a 3rd core required?
 
I just re-read your post reply, maybe this was an addition written after your initial post?? But this statement is totally Wrong! I'm not sure where your information is coming from, but the armouring of either 70C PVC or 90C XLPE 2 core SWA cables DO COMPLY for use as the CPC. 3 core 10mm SWA cables and above will comply with both equipotential bonding and CPC provision for the cable (Please check the sticky section on this subject (above) particually the tables in the link within post #37 by spinlondon)

I notice that you and some others, often use the term ''CPC'' when referring to equipotential bonding conductors. They are substantially different animals in fact, and perform totally different roles within an electrical installation and should never be confused with each other.

umm.....
I have looked at this 'sticky' post and it confirms what I have said. and is substantiated by the DNOs recommendations regarding the use of SWA's supplying external installations ( albeit back in the 80's).
10, 16, 25 mm2 2-core XLPE SWAs are insufficient to be be used as both a cpc and a MPB
I don't ever remember referring to a MPB as a cpc although they may have a duel function in regard to exportation of a PME supply.
 
umm.....
I have looked at this 'sticky' post and it confirms what I have said. and is substantiated by the DNOs recommendations regarding the use of SWA's supplying external installations ( albeit back in the 80's).
10, 16, 25 mm2 2-core XLPE SWAs are insufficient to be be used as both a cpc and a MPB
I don't ever remember referring to a MPB as a cpc although they may have a duel function in regard to exportation of a PME supply.


We must be looking at different tables then, as 2 core SWA cables will comply with CPC provision upto 95mm and possibly by calculation above!
3 core SWA armour cables from 10mm will comply with bonding and CPC requirements, ...bonding via the 3rd core, and CPC via the SWA. I have certainly not inferred that the Steel wire armour was of sufficient size to be used as a means of a combined bonding and CPC conductor!!!
 
We must be looking at different tables then, as 2 core SWA cables will comply with CPC provision upto 95mm and possibly by calculation above!
3 core SWA armour cables from 10mm will comply with bonding and CPC requirements, ...bonding via the 3rd core, and CPC via the SWA. I have certainly not inferred that the Steel wire armour was of sufficient size to be used as a means of a combined bonding and CPC conductor!!!

The RHS XLPE 2-core .... marked in pink
[h=3]Can we use the armour of an SWA as the CPC???[/h]It would help if I made a reference so that we can be clear about things
 
Last edited:
The RHS XLPE 2-core .... marked in pink
Can we use the armour of an SWA as the CPC???

It would help if I made a reference so that we can be clear about things

OK, Now i understand, the table you have been looking at can be a little confusing and often requires adiabatic calculation to confirm compliance. If you check this link out, as posted in ''Post 37 on this thread, ( steel wire armour as the earth conductor ) These tables are far more convienient to use, and are what i have been using for some years now, for a quick reference point to check SWA for CPC compliance...

It is well worth reading the whole of this article, as it can explain many things relating to the subject matter. The author of this article John Peckham, is a well respected Chartered Engineer.
 
OK, Now i understand, the table you have been looking at can be a little confusing and often requires adiabatic calculation to confirm compliance. If you check this link out, as posted in ''Post 37 on this thread, ( steel wire armour as the earth conductor ) These tables are far more convienient to use, and are what i have been using for some years now, for a quick reference point to check SWA for CPC compliance...

It is well worth reading the whole of this article, as it can explain many things relating to the subject matter. The author of this article John Peckham, is a well respected Chartered Engineer.

Thank you for this information. I can see there would be an element of confusion between the two tables.
However, I still find it interesting that the MEB would not allow the armour of certain sizes of 2-core SWA,s above 6mm2 to be used as cpcs.
 
The tables are a little misleading, all swa is now xple 90 C, so adjustments need to made to the tables. The restraints are more prevalent where conductor tempretures are upto the 90C.

Just work out the size of the protective conductor, bonding conductor using the tables or adiabatic, then apply the equation with the correct k values and cross reference with the manufacturers details.

Regards Chris
 
The tables are a little misleading, all swa is now xple 90 C, so adjustments need to made to the tables. The restraints are more prevalent where conductor tempretures are upto the 90C.

Just work out the size of the protective conductor, bonding conductor using the tables or adiabatic, then apply the equation with the correct k values and cross reference with the manufacturers details.

Regards Chris


Spin did send me an updated version by John Peckham, but couldn't find it. However what i remember of the tables, there was very little difference in them...
 
I always run a supply earth to out buildings un less we are specifically advised not to by the regs , i must admit i also never rely on the SWA as an earth i always use a cable incorperating a core that can be used as an earth and soley use the SWA as a meants of protection for the cable you cant beat a proper earth , when you do a caravan install using TT earthing the readings vary so much and i have had them going way over the 200 ohm limit in dry weather when it was wet it was less than 40 ohms so the earthing on a TT can be unstable and we all know how RCD can play up even the expensive ones ,an as i have said if TNS TNCS are permitted then that what ill install
 
This should be the updated version.
As far as I'm aware, it is only the Reg. Nos. that have changed.
View attachment 8067
This is the old one for comparison.
View attachment 8066

The issue with this table along with the ones in GN1 and GN8 is the incorrect K value seem to of been used.

The k value for the line conductors is given as 115(PVC) the problem is the standard now require XLPE for the line conductors. The K value being 154(XLPE)

So an example 2 core 120mm 115/51 x 60 = 135.29 but the insulation isn't PVC, its XLPE

It should be 154/51 x 60 = 181.2 mm, so you can see many sizes would not be adequate using the tables, the adiabatic may well prove otherwise.

The issue seems to of come about as the XLPE is rated to 90C, the problem is most of the time we work to 70C, they haven't included a K value for this scenario, so they used the PVC values, and they don't air on the side of caution.

Ill let you know the outcome, though i don't see how it can be incorrect, several cable manufacturers agree.

Regards Chris
 
Yes but no but.
Unless the equipment the SWA is connected to is rated at 90ºC, then the 70ºC tables would suffice.
 
I don't know why we keep harping on this 90C aspect for cables, it's highly unlikely that you'll ever see a 70C cable working at anywhere near that tempreture, let alone a 90C cable.
 
Last edited by a moderator:
Yes but no but.
Unless the equipment the SWA is connected to is rated at 90ºC, then the 70ºC tables would suffice.

The tables are using a k value for PVC, initial temp 70C and final 160C.

SWA no longer since 2008 utilises PVC for conductor insulation, so when calculating for short circuit we should be using the specific K value for that material.

XLPE, initial temp 70 and final temp 250 would give a K value of 154, so quite a difference. So as it stands i disagree with the tables.

Regards Chris
 
Just took the time to do a couple of quick adiabatic calc's using k=154 on these tables and well passed ( 120mm/150mm)
 
Just took the time to do a couple of quick adiabatic calc's using k=154 on these tables and well passed ( 120mm/150mm)

But what level of fault current did you use for the adiabatic, im not disagreeing with the fact the cable is protected, just the tables are not correct.

As long as I2T is less than K2S2 then there's no issue, also taking into account the magnetic effect of the armouring.

It was just the case id worked out some values and cross referenced them with the tables and noticed a difference, then realized they had used K values for PVC. Reality is as you say using the adiabatic they will be ok.

Regards Chris
 
I was under the impression if it was a PME head you was not supposed to extend the earth to the out building but just use a 2 core and stake the out building with an electrode, this was told to me by my 2391 tutor when I was on my course. Is this right or wrong, either way can you point me to the reg in the BRB that states it.

Cheers

ICE
 
I was under the impression if it was a PME head you was not supposed to extend the earth to the out building but just use a 2 core and stake the out building with an electrode, this was told to me by my 2391 tutor when I was on my course. Is this right or wrong, either way can you point me to the reg in the BRB that states it.

Cheers

ICE

A 2391 tutor who believes in mythology?....the mind boggles.:uhoh2:
 
Well what ICE was saying was what I was getting at in a way, except it the install is a TT system at origin do you run a 3 core to the outbuilding carrying a CPC as one of the conductors or do you run a 2 core and put an electrode in at the out building connecting to the sub mains there?
 
Well what ICE was saying was what I was getting at in a way, except it the install is a TT system at origin do you run a 3 core to the outbuilding carrying a CPC as one of the conductors or do you run a 2 core and put an electrode in at the out building connecting to the sub mains there?

Why would you want to isolate a TT system earthing system?? If anything you would want to connect the 2 rod positions together giving you a theoretical better/lower Ra level for the installation as a whole!!
 
Agreed Engineer. If the reading on the rod at the sub building is low. In this case 18 ohms. Would I be right in saying that no regs would be broken if a 2 core cable is used to save on cost?
 
Agreed Engineer. If the reading on the rod at the sub building is low. In this case 18 ohms. Would I be right in saying that no regs would be broken if a 2 core cable is used to save on cost?

No Reg's will be broken, but will in my opinion be a false economy!! The cost of a 3 core cable is not going to be that much more than a 2 core...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earths at outbuildings...
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
69

Advert

Thread statistics

Created
Boberto,
Last reply from
Engineer54,
Replies
69
Views
21,384

Advert

Back
Top