As ive always understood it if you were to run a SWA to a garage / shed, lets say 30m away, and if the earthing system at the origin (house) is tncs then a earth rod would need to be installed at the outbuilding because tncs/pme cannot be exported.
Where the earthing system at the origin is a tt system am I right in saying that an earth rod can be installed at the out building especially if Ze readings on the rod at the house are particularly high. If this is the case would a 2 core cable suffice as a supply to the outbuilding or would a 3rd core (earth) be advisable (belt and braces)???
What is the norm with a tns system? Export the earth or install earth electrode at outbuilding?
Ive just read this back to myself and I havent worded it brilliantly, and its late, and i've been on the Coors so apologies for being a thicko.
Exporting the PEN or the earth part it has been viewed with concern in this country primarily because the rise in voltage potentials on the neutral (unbalanced 3-phase loading under normal conditions) and hence on the earth. Under supply fault conditions this potential will become very high (supply potential on single phase systems .
In the UK the IET have recommended that an earth electrode is provided at the MET to protect the installation to clamp the fault voltage to earth potential but can give rise to another problem such as high circulating currents. However, this was part of a wiring Matters article written a few years ago and is not explicitly stated as part of the regulations.
So IMO there are two concerns
1/ If you export the cpc it must first be able to cope with the possible fault currents (adiabatic)
It is unlikely that the armour of the SWA cable will be able to provide a low enough Zs value on its own, but might be Ok with the use of an RCD.
However, if you separated the earthing arrangements, by bonding the armour at the MET only and used an earth electrode at the point of utilization (outbuilding) Your main method of protection will be by the RCD and will allow you to have a much higher Zs in which case you would only need a 2-core cable
2/ Exporting the cpc away from the equipotential bonding zone to structures containing extraneous conductive parts.
It would be unwise to export any cpc where there is the possibility of external extraneous metalwork because of unaccountable or 'unknown' network faults which would include high resistance or loss of neutrals . In this case your earthing system would carry all of a proportion of the lost neutral currents from your neighbour's installation downstream of the network fault .
If you choose this method then I would recommend that you size the cpc to the same size as stated in BS7671 table 54.8 with a minimum of 10mm2. In which case you would be wise to use a 3-core cable equal to or larger than 10mm2