Earths at outbuildings...
What's wrong with what i wrote about outbuildings with extraneous conductive parts, that's basically what's stipulated in the Reg's. What i don't, and will never understand, is why would anyone ditch a superior earthing system, in favour of a TT system with an Ra of around 200 ohms. The ONLY time i would even consider doing that, is if the financial aspects made it literary non-viable
Hey ho, another week, another PME post-E54 is absolutely spot on in the post above-with the obvious exceptions listed in BS7671:2008 there is rarely a case (other than economic) for not using the suppliers earth connection.
The PME system has been adopted throughout the developed world and continues to be an economic and safe method of distribution.
On the other hand, a quick read through many posts on this forum indicate the lack of understanding and mystery surrounding the regulations and installation methods of a TT system!
I'm currently writing a FAQ sheet on TT system installations for a certain electrical publication, I'll post it up on the forum for comment before it's submitted.
Well for one thing, i would never walk away from any TT system that was only giving me an Ra of around 200 ohms, by the time i walked away it would be substantially less!! lol!! And talking of costs, ....It could well end up costing more to install a decent TT system than running that main bonding cable, in the time taken!!
By the way, there is nothing to stop you including a rod at the outbuilding, it will help clamp the touch voltage. But personally i wouldn't find it necessary to do so, i'd be quite happy with the PME/TNC-S at the outbuilding, whether it has extraneous parts or not!! lol!!
Im now worried about these extraneous conducive parts, my house is pme and i have lots of extraneous conductive parts inside, do i need to TT the installation ? :)
Ha, summed up perfectly!
I’ve finally got the solution to this. Jack the house up, have it mounted on glass insulators, an isolation transformer in the garden. Each of the front steps will have to be insulated from each other. Totally earth free!
Looks like we are in need of another amendment :) .
Well for one thing, i would never walk away from any TT system that was only giving me an Ra of around 200 ohms, by the time i walked away it would be substantialy less
E54,I'm interested to know what value of Ra you would accept.given that a 30ma RCD will provide earth fault and additional protection up to 1667 ohms..(in theory!)...why is an Ra of 200 ohms not acceptable?
Unless you achieve an Ra of <5 ohms ,for example,the typical OCPD,s on final circuits will not reliably operate in an acceptable time under earth fault conditions. Therefore you are likely to be reliant on the RCD.
It seems to me that the RCD will operate in exactly the same way whether the Ra is 5 ohms,or 200 ohms.....so why bother with 5 ohms?
The question I am asking is what is your maximum Ra....and why that value?...discuss....:smilewinkgrin:
There's nothing to worry about, as long as
1/ Main Protective Bonding is in place and IS effective (Not connected to internal plastic pipework :) )
2/ the simultaneous touchable extraneous parts are connected together (usually now only bathrooms and the like)
You are now in a Faraday's Cage
Connecting an earth electrode to the MET will reduce the possible DNO's fault voltage and your Faraday's Cage to something around ground potential, bus as already stated, you might be supplementing the network return currents via your electrode.
Am I losing the plot here or what
The earthing arrangement is at the ORIGIN in this case a TNCS
PME relates to multiple earthing on the DNO network
The S in TNCS stands for separate CPC after the service head
So why install an extra Electrode at an outbuilding if the sub feeder has a separate CPC that is correctly sized
I agree to ensure extra safety an electrode can be installed at the origin connected to the MET if there is an appreciable risk the incoming PEN may be broken IE overhead 2 core supply.
Sorry for the delay in replying wirepuller, i fell asleep as i'm also up-dating my monthly project report, i just keep the forum running in the background, and come back from time to time when i need a break. ..lol!!!
Let me start of by saying that i don't particularly like to see a TT system on domestic installations full stop, especially in the UK!! The art of creating a good TT system there, seems to have been lost since it was common practice in the rural and suburb areas of towns. Then it was common practice to aim for a 10 to 25 ohm Ra and depending on the sparks, ...often achieved better. These day's it's just not economically viable in many cases on a domestic installation, But that's not to say that a decent attempt should not be made, by at least using a DEEP driven rod, of a suitable depth and not just bunging in a super thin 1.2m rod in the ground, that in all honesty is a total waste of time!! ...
What i personally try and achieve on a TT system is a low enough Ra to trip a socket circuit on say a 16A/20A MCB, in several seconds and lower rated MCB's in 5 sec, (although an MCB can trip anywhere on the instantaneous portion of it's T/C characteristic) which was a little easier on the older type 1 MCB's and BS 1361 fuses, than it is with the new type B MCB's.
I'm not trying to meet the new or old TT system disconnection times, based on RCD protection. I would however be trying to give the installation a degree of protection should a RCD fail for whatever reason, ie ''Addition Protection''. We must also remember that disconnection times rely on the installations Zs and not necessarily on the Ra/Ze alone when a RCD fails.
I've never said that installing a good/decent TT system is going to be cheap, it's not, certainly not in the time taken to install one. Depending on the soil resistivity and conditions, could further add to costs, in terms of materials... However, i'm fairly confident that given say 4 X 3m 3/4'' rods i could achieve an Ra value of 3 to 5 ohms in many parts of the UK, and in some area's that i know, below 1 ohm, with less rods. Depending on the soil conditions, that may well also require electrode enhancers and/or modern soil conditioning chemicals.
So what does a 200 ohm Ra give you?? Absolutely nothing really, ...It achieves a 50V touch/threshold voltage, only while a 30mA RCD is functional!! The lower the Ra, the better the chance of limiting the touch/threshhold voltage that will be present in a fault condition... I can't say i know of any other national code or Reg, that has such a high max Ra value of 200 ohms. The States and Canada require 20 ohms, even France wants to see a max of 100 ohms, and they use 500mA RCDs on domestic installations....
As it so happens, we are in the final throws of completing a number of ground fields on my project, with a contract specification level of max 1 ohm for each of the ground fields, which was achieved on all of them, before all of the rods being placed. The highest ground field to date, coming in at 0.38 ohms and when all are connected together by a site ring (before connecting all project buildings) of 240mm, i've roughly calculated a final Ra of around 0.17ohms. OK, so i'm far happier working with extensive TT systems, than the much smaller ones, but even they can be made/designed to provide a decent and stable measure of protection. As mentioned earlier, it just depends on how much time and of course money you, and the customer wants to invest in the installation. I know what i've managed to achieve with relatively little monetary cost, but with a fair bit of time at my house in Cyprus and with pretty bad soil conditions too, (soil resistivity of 650+ ohm/m). (in
I know full well that you disagree on the value a good TT system can bring to an installation, based on the time and cost, and that you would prefer to trust that RCD totally, to provide your earth fault current protection, whereas i wouldn't. Which is why it is better to agree to disagree, because i'm sure we are not going to change our thinking on the matter...lol!!!
Thankyou for your very informative reply E54....I would entirely agree with you that if an Ra of substantially less than 10 ohms,or even TN values of Ze can be achieved then the OCPD operating in case of RCD failure within a reasonable time would be an advantage.....I think though,as you imply,on the typical small TT install usually queried on this forum such values are not practical or cost effective.
My argument is with "higher" low values which some people insist should be aimed for,such as the 25 ohm vaue you gave as an example. Such a value would give you an PEFC of 9.5A on a 230v supply....that wont trip a 32a mcb and would take around 400s to trip a 6A/B......not much use really. Therefore you are still dependant on the RCD,so what is the advantage over an Ra of 200 ohms?...personally I cant see one.
To sum up I totally agree that low enough Ra's to operate an OCPD quickly are an advantage....but Ra's still considered low, but way to high to operate an OCPD are a waste of time and money trying to achieve as they offer no advantage over Ra's of 100-200 ohms.
I can see where your coming from, i can honestly, but don't just think in terms of ultimate Ra values. A good Ra value will almost certainly help in Zs values in the smaller TT systems so a stable 20/25 ohm Ra can and will help disconnection times that are based on Zs values. It will also go a long way in clamping or limiting the touch/threshold voltage. Every installation is going to be different, it just needs a level of competency to access and provide each installation with at least a working earthing system and not a dormant one.
I can't see why, the installation of a decent length of earth electrode can't be a dam site more beneficial than installing a earth rod that is too short and too thin to give an installation any overall benifit or any longevity. For sure, they will never in a month of Sunday's provide a stable Ra value, it's will be up and down more times than a ------ draws during the course of a year!! lol!! For me, they should either be removed from the market place, or an Ra level set, that would make them impossible to comply to the requirements.
Just a small point
XLPE SWAs are used now in the UK more and more, Any (most) sizes larger than 6mm2 will not comply with fault protection which means that the maximum size realistically would be 6mm2 and then you would have to run a separate protective bonding conductor .
I just re-read your post reply, maybe this was an addition written after your initial post?? But this statement is totally Wrong! I'm not sure where your information is coming from, but the armouring of either 70C PVC or 90C XLPE 2 core SWA cables DO COMPLY for use as the CPC. 3 core 10mm SWA cables and above will comply with both equipotential bonding and CPC provision for the cable (Please check the sticky section on this subject (above) particually the tables in the link within post #37 by spinlondon)
I notice that you and some others, often use the term ''CPC'' when referring to equipotential bonding conductors. They are substantially different animals in fact, and perform totally different roles within an electrical installation and should never be confused with each other.
on a tt installation can you run a 2 core cable to the shed and drive another spike in the ground outside the shed? If you do this is a 3rd core required?
Boberto,
Engineer54,