earths?? | on ElectriciansForums
Discuss earths?? in the Australia area at ElectriciansForums.net
G
gpz900jim
I have to fit a power shower as a replacement to an existing one. The shower is rcd protected, measured zs reading is within acceptable limits, for a 0.4 second disconnection time, but the main earthing conductors to the gas and water are not up to current spec. Will I have to change them? or will they be ok left, given that the zs is ok?? cheers jim
If it is not an identical replacement ie addition or alteration then yes you have to upgrade earth and bonding. If it is an identical replacement and the present bonding/earth show no sign of of overheating and were correct at time of previous install i believe it is not an absolute must - however i would encourage the client to upgrade.
Reply to earths?? in the Australia area at ElectriciansForums.net
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...