I disagree. There is a box especially for detailing what the condition report is for. Put in there “to determine dead installation is safe to be made live by the DNO”.

This then spells out clearly what the report is for and would make it clear why the excessive limitations.

It would aslo make sure the report could not be misused by the owner.
If you look at the notes for EICRs on the model forms, it clearly states the report is to confirm where reasonably practicable that the installation is in a satisfactory condition for continued service.
If this inspection is to be conducted in accordance with BS7671, the very first thing to be done is to visually inspect the condition of all electrical equipment which is not concealed.

God forbid that after failing to spend 10/15 mins looking round the place and you sign off the installation as being safe to energise, that someone is electrocuted due to bare conductors hanging out of a wall or ceiling, or exposed by a broken socket front plate.
Seriously, are you not going to walk around and count points served, or confirm circuits?
 
If you look at the notes for EICRs on the model forms, it clearly states the report is to confirm where reasonably practicable that the installation is in a satisfactory condition for continued service.
If this inspection is to be conducted in accordance with BS7671, the very first thing to be done is to visually inspect the condition of all electrical equipment which is not concealed.

God forbid that after failing to spend 10/15 mins looking round the place and you sign off the installation as being safe to energise, that someone is electrocuted due to bare conductors hanging out of a wall or ceiling, or exposed by a broken socket front plate.
Seriously, are you not going to walk around and count points served, or confirm circuits?

Of course you would. In order to complete dead test you would dommost of that anyway.

Is that what is being debated?
 
Seen it a few times before, usually goes like this.
Letter received from DNO
"Dead testing MUST be completed and a copy of the test results MUST be made available for the engineer on the day of connection otherwise connection cannot proceed"

Day of connection, to DNO engineer
"Hi mate, got your test results you need"
"My what ?, nah mate I don't need any of that. Where's the head going ?"
 
So the report is done and let's say that a C2 is found. Would DNO refuse to connect? Assume C3 is ok to connect and C1 not ok. Just wondering :)
 
You could do a EICR dead using R1R2 and IR (where possible), any circuits not passing muster could be left disconnected with the prior agreement of the client (you could make this a condition of the works)
Worst case - they could be left with a install with adequate bonding and 90% of the circuits not connected :D

From past experience- if it is not connected they deal with it sooner rather than later
 

Reply to ECIR requested by the supplier. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top