the following was faound:

1) Outside adaptable box had a large piece missing from the front,
2) Socket Upstairs was damaged showing copper
3) Earth stake was giving a reading of 425 Ohms (Couldnt even find stake if there was one! i predict under the floor which has since been covered)
4) RCD Not functioning properly. Tripped on half reading and during Zs tests even though my meter should prevent this.

1) C2 unless live parts can be touched directly by hand then C1
2) C1
3) C3
4) C2
 
I would give item 3 a C2 with further investigation as the reading for the earth stake is way to high agree with biff on items 1,2 and 4 though
 
4) RCD Not functioning properly. ---- C2

Interesting one. If you aint got any RCD's protecting your installation its only a C3 --- unless its forming part of a TT system or for sockets liable for outside use?

I haven't seen anything suggesting a failed RCD should be a C2 but you could well be correct!

Can anyone throw any definitive guidance as to why its a C2 --- not trying to be contentious here for a change, just for my own edification.
 
Interesting one. If you aint got any RCD's protecting your installation its only a C3 --- unless its forming part of a TT system or for sockets liable for outside use?

I haven't seen anything suggesting a failed RCD should be a C2 but you could well be correct!

Can anyone throw any definitive guidance as to why its a C2 --- not trying to be contentious here for a change, just for my own edification.

As the mention of an earth stake I would of thought it was A TT system Hence the C2
 
As the mention of an earth stake I would of thought it was A TT system Hence the C2

You're right, I knew and gave the answer in my response but didnt read the question correctly!

So to re-phrase my question, if it wasnt a TT system and the RCD failed what would the code be?
 
So to re-phrase my question, if it wasnt a TT system and the RCD failed what would the code be?
Damn, should have engaged brain before posting that question but in my defence I have been drinking and watching a fine Scarlets rugby win!

If the RCD dont work then effectively you aint got RCD protection so all those rule for C2/C3 apply .....
 
Interesting one. If you aint got any RCD's protecting your installation its only a C3 --- unless its forming part of a TT system or for sockets liable for outside use?

I haven't seen anything suggesting a failed RCD should be a C2 but you could well be correct!

Can anyone throw any definitive guidance as to why its a C2 --- not trying to be contentious here for a change, just for my own edification.

following the general drift of the ESC code guide , C1's are pretty much reserved for items that could cause immediate injury or fire risk.
a faulty rcd doesnt fit that bill really.
in terms of severity , it has "potential" to be a risk rather than be an immediate danger , hence C2
 

Reply to ECR Unsatisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
408
Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top