Howdy folks.
I have just been reading the exam success book and according to the book the best way to conduct an EFLI test on a TT installation is to isolate at main switch, close all circuit breakers remove main earth terminal and then connect earth lead of tester to disconnected main earth conductor, neutral to consumer side neutral IE isolated side of main switch and also line to consumer side line IE isolated side of main switch then switch on the main isolator and test.
This makes sense from a safety stand point as you will not be sticking your fingers near any live conductors.
My question is if I were to do an EFLI test at a remote lighting point would I isolate the supply with main switch. close all circuit breakers, close board and lock it, walk back to lighting point, attach my tester, place loads of warning signs around it then walk back to the board and switch on, walk back to my tester test then walk back to the board switch off then walk back to my tester and remove it.
I mean this seems more dangerous than just connecting my tester to the live connections inside the lighting point IE inside the ceiling rose or whatever.
What do you think would be the safest way to do an EFLI test at a remote lighting point?
Surely walking backwards and forward to the board or even a lighting switch and leaving your tester, ladder , exposed conductors would be more dangerous than just working live in this instance.
Maybe if you put on a pair of insulated gloves or something when connecting your test instrument, maybe this would make them happy.
Any thoughts on this one.
Thanks.
I have just been reading the exam success book and according to the book the best way to conduct an EFLI test on a TT installation is to isolate at main switch, close all circuit breakers remove main earth terminal and then connect earth lead of tester to disconnected main earth conductor, neutral to consumer side neutral IE isolated side of main switch and also line to consumer side line IE isolated side of main switch then switch on the main isolator and test.
This makes sense from a safety stand point as you will not be sticking your fingers near any live conductors.
My question is if I were to do an EFLI test at a remote lighting point would I isolate the supply with main switch. close all circuit breakers, close board and lock it, walk back to lighting point, attach my tester, place loads of warning signs around it then walk back to the board and switch on, walk back to my tester test then walk back to the board switch off then walk back to my tester and remove it.
I mean this seems more dangerous than just connecting my tester to the live connections inside the lighting point IE inside the ceiling rose or whatever.
What do you think would be the safest way to do an EFLI test at a remote lighting point?
Surely walking backwards and forward to the board or even a lighting switch and leaving your tester, ladder , exposed conductors would be more dangerous than just working live in this instance.
Maybe if you put on a pair of insulated gloves or something when connecting your test instrument, maybe this would make them happy.
Any thoughts on this one.
Thanks.