Question:
Describe in detail how to carry out by direct measurement an earth fault loop impedance test on the workshop lighting circuit.
Answer:
secure safe area around last luminaire on the circuit.
Test instrument to be used is an earth fault loop impedance tester.
Leads to GS 38.
At the furthest point on the circuit test between switched line and CPC.
With the circuit energised test and record result.
Re-instate luminaire.
Now that all sounds a bit vague to me.
Test between switched line and CPC, what with the circuit energised, do I connect the leads with the circuit on or off.
It's a very vague answer.
Other question:
Describe the test procedure to determine the resistance of the installation earth electrode.
Answer:
seek permission to isolate.
Safely isolate supply and all circuit breakers.
select and earth fault loop impedance tester confirm calibration condition of leads to GS38.
disconnect the earthing conductor from the main earthing terminal.
connect the instrument earth lead to disconnected earthing conductor, neutral to outgoing neutral of main isolator, line to outgoing line of main isolator.
close main isolator.
check instrument set to 200 Ohms and carry out the test and record the result.
Open the main isolator and disconnect the instrument in the reverse order.
Reconnect the earthing conductor.
I always thought a person would do the test at least twice to check for voltage spikes or transients, maybe C and G don't like this method.
My point is in the second question the book answer makes a strong point of connecting the leads when the circuit in safely isolated but on the first answer, the light test there is no mention of isolating the supply to connect the test leads, that fact is brushed over if you ask me and the answer is very vague.
I just wonder what you guys who do this sort of test in the real world would do and what you would consider to be safe.