malcolm, thet are going back to the megger LT5 which had a slider switch to select range. 20ohms or 200ohms. and i would agree that the no-trip should not be used for Ze. they state a pfc of over 1kA if that is pefc, then it must be a bloody long rod.
Hi mate the 100mA rcd which serves as a isolator also would be switched off and to carry out the test this would be done on the supply side with isolator/rcd off and all loads removed then disconnect earthing conductorHere's another one:
"The installation forms part of a 230V, 50Hz TT system with a PFC of 1.3KA.
A 100ma RCD, which also serves as the main isolator, is installed in the consumer unit."
Describe the test procedure to determine the resistance of the installation earth electrode.
Book answer:
1. seek permission to isolate.
2. safely isolate supply and all circuit-breakers.
3. select an earth fault loop impedance tester, confirm calibration, condition and leads to GS38.
4. disconnect the earthing conductor from the main earthing terminal.
5. connect the instrument, earth lead to disconnected earthing conductor, neutral to outgoing neutral of main isolator and line to outgoing line of main isolator.
6. close main isolator.
7. check the instrument set to 200 Ohms and carry out the test and record the result.
8. Open main isolator and disconnect instrument in the reverse order.
9. reconnect the earthing conductor.
Now I am no expert but would this not trip the RCD which is incorporated in the main isolator?
I mean we are allowing current to flow from the line over to the earth, surely the RCD will see this as an imbalance between line and neutral and switch everything off.
Any thoughts?
Thanks.
Hi mate the 100mA rcd which serves as a isolator also would be switched off and to carry out the test this would be done on the supply side with isolator/rcd off and all loads removed then disconnect earthing conductor