Measure.

It is possible that your low current Continuity tester will indicate a sound connection, whilst the high current Loop Impedance tester will expose a possible weakness.

Regards

Billy
 
If you've proven continuity and measured your Ze, then calculating Zs is fine by me. But it actually doesn't take that long to measure, so I suppose you just get better piece of mind by doing so.
 
We discussed this a day or two ago and decided to verify the circuit a measured ZS was needed, can't remember which thread it was now but it made sense afetr reading it all.
 
And that's why it's better to calculate.

Parallel paths come and go, and you have already proven you have an earth so I don't agree with you at all.

I do agree with this reasoning, and as a rule I tend to calculate. If there's a lot involved with disconnections for measuring, however, I'll happily measure.
 
Time to be contraversual (if I could spell it). So I'm spurring off a RFC. I take the Zs at the "donor" socket, then do a R1 + R2 on the new bit. This to me is OK, but many would say you HAVE to do it from the board - WHY?
 
Time to be controversial. So I'm spurring off a RFC. I take the Zs at the "donor" socket, then do a R1 + R2 on the new bit. This to me is OK, but many would say you HAVE to do it from the board - WHY?

Depends on how long the spur is...





having already verified the original cct.:)
 
Always measure the Zs as this is the only test that verifies the complete circuit. To throw in my scenario from the other day with a protective device with a high internal resistance.
 
So as the MWC/EIC needs an R1+R2, how would you arrive at that? It shouldn't be done as Zs-Ze due to parallel paths. Measurement is great for circuit confirmation, but for the paperwork?
 
It is all well and good calculating it, but it doesn't prove that you have an earth, testing it does. I know calculation is acceptable, but measurement is better if you think about it, and although Ze =Zs +(R1+R2], a measured result will always be a bit lower (or should be) due to parallel paths, and the current that the tester is forcing around the circuit.

Cheers……………..Howard
I too disagree with SirKit! Its Zs = Ze +(R1+R2) :devilish:
 
just as a slight digression, yesterday was testing an existing efli on a lighting circuit. using 1553 on no-trip. MFT came up with "trp" and the RCD had, in fact, tripped. i can only assume a poor lead connection. any other thoughts? the RCD had been tested and gave ideal results on both x1 and x5. ( 34mS and 12mS).
 
just as a slight digression, yesterday was testing an existing efli on a lighting circuit. using 1553 on no-trip. MFT came up with "trp" and the RCD had, in fact, tripped. i can only assume a poor lead connection. any other thoughts? the RCD had been tested and gave ideal results on both x1 and x5. ( 34mS and 12mS).

I've had this before on my 1730. Usually existing leakage+test current pushes the RCD past it's limit (usually around 22mA on a 30mA unit).
 

Reply to EFLI - measure or calculate? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
255
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top