BS7671 does not specifically state an rcd must be used for fault protection in a TT system although it is preferred. An overcurrent protective device may be used alone provided a suitably low value of Zs is permanently and reliably assured, see Regulation 411.5.2.
In an era when BS3036 semi-enclosed fuses were the norm then a 5A fuse in todays standards has a maximum Zs of 9.10 ohm.
 
I thought we’d arrived at it being ok to use a tails gland and tails clamp and bring the tails straight in?
As far as I'm aware this is acceptable. It best be as it's what I do... ?
 
I might be misunderstanding your point.
Lots of properties near me are TT with double insulated tails going into a plastic CU with an RCD main switch.
Come the day these are upgraded to an new and obviously metal CU, I thought we’d arrived at it being ok to use a tails gland and tails clamp and bring the tails straight in?
A while back there was a debate that an up front RCD would need metal containment in 18th and the problem simply moved.
Or have I misremembered the conclusion from the pages of debate?!
I think what I meant to say is that you would have to take extra precautions to mitigate the possibility of a live to earth fault occurring within the consumer unit, if the consumer unit is metal, and the tails are not RCD protected. As opposed to not worrying about it with a plastic consumer unit. My apologies for not typing out what was in my brain!
 
Pre metal consumer unit it was a big no no to fit a metal enclosure consumer unit without rcd protection to its supply on a TT but now it seems okay, the times a changing.
But how many times did people use tails clamps/glands etc to mitigate the risk?
 
But how many times did people use tails clamps/glands etc to mitigate the risk?
To me that is the key factor - some additional clamping so tails being wagged does not result in them loosening from the incomer, and the entry glands seem the perfect way of dealing with that and the risk of insulation being cut on the case edge.

Also said incomer's screws correctly tightened. And checked after a wiggle.

Even so, if it were me I would still like to see a 100mA delay RCD up-front even with an all RCBO board to eliminate a single point of failure in the electronics.
 

Reply to EICR 100ma RCD TT systems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
521

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top