Hi,

My EICR is a C2 because the consumer unit does NOT have RCD's.
Is it correct?
My last EICR five years ago stated RCD as recommended.
What's changed?
The flat is on the 2nd floor built in 1997!
The electrician has quoted for a NEW Consumer Unit.

Thanks

Victor
 
If there was no supplementary bonding in the bathroom or RCD protection to the circuits that warrants a C2
Exactly what i was thinking!
[automerge]1593541730[/automerge]
Some of our tenants have the mem boards fitted in 2005 or before . Ones where some is rcd protected other half isnt. When doing eicrs its a c3 that cables less than 50mm are not rcd protected and also c3 that lights arent rcd protected.
If however we want to do work on these circuits we either swap the mcb for an rcbo or move the mcb over to the rcd side.

As for an upfront rcd not being compliant...so you have a client with an old cartridge fuse board asking you to put an extra light on the circuit...not that big a job...you're going to honestly turn to them and say
Yeh well first im going to have to test the whole install as i have to change the whole board.
As i suspect dave from the pub would soon happily be used instead
[/QUOTE
I use an rcd fcu
 
No it’s not correct.
There is no requirement to install RCDs in Consumer Units.

There are requirements to protect some circuits, which would require an RCD be placed in or very close to the Consumer Unit.
However, the person who conducted the Inspection should be listing the instances where RCD protection is required but not been provided, and then applying a code for each of those instances.

In many instances, RCD protection can be provided, simply by the installation of an RCD or RCBO in or close to the Consumer Unit.

Only thing that’s changed, is the person who conducted the latest inspection, wants to make money from you.
Hi been using the Napit Code breaker for a few year now and if I see none or a lack of RCD protection for circuits not clipped direct or in trunking or conduit its a straight C2
just on the grounds of section 5.12.3, 522.6.202, no protection of cables in wall less than 50mm from surface, which can not always see but can assume if the wall is a standard 100mm wall, that it does not conform, we sparkies are not looking to rip people off as Ive seen peeps on here giving good sparks a bad name on for telling folks you got to spend money on your property to get it to a good and safe standard etc. as introducing RCD's or RCBO's also detects any Earth to Neutral defects if not already identified on the EICR
this is just my opinion and my clients will have a chose to do it or not.
Regards Jelade Electrical Services
 
Hi been using the Napit Code breaker for a few year now and if I see none or a lack of RCD protection for circuits not clipped direct or in trunking or conduit its a straight C2
just on the grounds of section 5.12.3, 522.6.202, no protection of cables in wall less than 50mm from surface, which can not always see but can assume if the wall is a standard 100mm wall, that it does not conform, we sparkies are not looking to rip people off as Ive seen peeps on here giving good sparks a bad name on for telling folks you got to spend money on your property to get it to a good and safe standard etc. as introducing RCD's or RCBO's also detects any Earth to Neutral defects if not already identified on the EICR
this is just my opinion and my clients will have a chose to do it or not.
Regards Jelade Electrical Services
This is at odds with Best Practice Guide 4, which codes it as C3
 
This is at odds with Best Practice Guide 4, which codes it as C3
Yet Napit , Niceic and others sit on the electric safety first committee that write up these best practices guides and are supposed to come to a mutual agreement , yet Napit C2 this in their own guide book? Bizarre!
 
Hi Everyone.

I have done an EICR at a cleaning company today. The installation is less than a year old as they have had a refurb. The spark who did was retired and wouldn't issue any certification! In fairness the job is to an ok standard but there isn't any RCD protection on anything. Am i correct in thinking that because it was 'designed' under 7671:2018 that it is a C2? or would C3 still cover it?
 
Hi Everyone.

I have done an EICR at a cleaning company today. The installation is less than a year old as they have had a refurb. The spark who did was retired and wouldn't issue any certification! In fairness the job is to an ok standard but there isn't any RCD protection on anything. Am i correct in thinking that because it was 'designed' under 7671:2018 that it is a C2? or would C3 still cover it?
The date it was designed has absolutely nothing to do with how safe or dangerous it is.

You need to make that judgement.

Dates are wholly irrelevant.
 

Reply to EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
670

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top