Oh this has got a bit long.
If that isnt fault protection (shock) what is it? Protection against thermal effects, overcurrent, voltage or electromagnetic disturbances? Or is there some other protection for safety in the BGB that supp bonding is and I've missed? (415.2 note 1 also mentions supp bonding being an addition to fault protection)
Well, that's just the definitions.
OPDs protect against faults by disconnection. SB protects a person until disconnection but does not and cannot clear the fault.
[/QUOTE]The accepted safe voltage is 50V therefore this impedance must be below 50/Ia. See 415.2.2
No problem with that, reg 415.2.2 as you state[/QUOTE]
But you are arguing that this is not good enough and the 'below 50/Ia' must be reduced by more bonding.
Is that a direct quote from the BGB? -- if so please point me to the reg as the only regs I can find are in 701 stating supp bonding must be in place and 415 where it states what must be supp bonded and how you can use the 'equation' to confirm the effectiveness of this supp bonding when in place. I cant find anything that states that if the 'equation' value is greater then only then, and then only, must supp bonding be installed?
It states that the value must be below 50/Ia so if it is higher SB is required, if it is lower it is already ok.
E.g. you cannot 'see' any SB between two pipes but the measurement is 0.05, are you going to add SB so that it is 0.01 even though 200A x 0.05Ω = 10V.
Totally disagree, supp bonding is a requirement under 701/415 regardless of readings.
No, the readings are the determining factor. <=50/Ia is satisfactory.
What is the point of the measurement if you had to ensure 0.05Ω
The regs allow supp bonding to be either in the bathroom or close to where the 'extraneous' parts enter the bathroom. Whether you can combine supp bonding and main bonding as the same thing just outside the bathroom sounds like another thread to discuss! Ive never thought of it like that but I can see its merits!.
Would you demand two conductors in parallel?
What would be the point?
The main bond does not need (require) supplementing.
New one on me! I know you can use the CPC of attached equipment as a bond (544.2.5) but didnt know a pipe was an acceptable conductor alternative. Where is this pipe as a bonding conductor defined?
543.2.1(vii)
Thats not the point of supp bonding -- to connect to the MET. Its to connect all the 'extraneous parts', 'protective conductors' etc ... together in the bathroom to form I guess a faraday cage? But you raised an interesting point before, can the supp bonding and main bonding be one of the same thing when just outside the bathroom
No, but the extraneous parts must be 'effectively connected to the MET'
I think it does matter what is causing the reading ..... the definition is in 701 that supp bonding must be in bathroom (or close by) and 415 which defines a physical connection between all the bits, the effectiveness of this connection being proved by the 'equation'. Again if there is a reg that over rides these requirement then please quote. Or if my interpretation of what the regs state is clearly wrong please define which part supports your arguement.
What do you mean 'if there is a reg that over rides these requirement then please quote'?
That is what I have been saying all along.
You are again forgetting the 'if required bit'.
If the measurements are within the safe limit (50/Ia) then the parts are proved to be effectively connected.
No arguement from me there. Totally correct statement!
But you have been arguing that it is necessary whether required or not.